  1. #1
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52

    Can someone check my code?

    I am setting my ato up for a different setting. I have Kalk in my ATO and want to stabalize my PH. it sits good all day and drops at night, so I am thinking I would like my ATO to only work between 8:30pm and 7:00am does this code look like it will work?

    FALLBACK OFF
    If Sw1 OPEN Then OFF
    IF TIME 7:00 TO 20:30 THEN OFF
    OSC 00:00/15:00/45:00
    Defer 005:00 Then ON
    Defer 000:10 Then ON

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Youve got two defer statements both for on. Was one supposed to be a defer off statement?

    In order to truly check this, I also need to know what the flowrate of your pump is and you typical daily evaporation loss.

    Anyone who cannot cope with mathematics is not fully human. At best he is a tolerable subhuman who has learned to wear shoes, bathe and not make messes in the house. -robert heinlein

  3. #3
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    My flow rate is a max 115 gph or so from the pump, and I use maybe 10 gals avert week or 2
    The defer was to delay start and prevent short cycles while running

    Sent from my ADR6350 using Tapatalk 2

  4. #4
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,495
    The If Swi1 and If Time statements must come after the OSC line. OSC has both ON and OFF states, so those If statements will be ignored the way you have it.

    You cannot use two Defer ON statement in one outlet program. As zombie asked - is one intended to be Defer xxx Then OFF?
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  5. #5
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    I am just a bit confused there. If the float switch triggers, between the hours of 8:30 PM and 7:00 AM, then turn on the pump. Should I scrap the OSC and defer commands?

  6. #6
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    I just created a how to guide that goes into a very reliable version of what you are trying to do here. I have the link below. I would strongly recommend getting a lower flowrate pump like an aqualifter or peristalic dosing pump. the one you have is going to add kalk way to fast to the point that you may be killing corals (believe me I have done it before when I used a pump about the same size).

    http://forum.neptunesystems.com/show...5978#post35978

  7. #7
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    I tried aqualifters (3 different on a JBJ ATO) and they were by far the worst most useless pumps I have ever run since I started salt 25 years ago. I would rather hand dose than use them. But I guess I will just go with this code

    Fallback off
    If time 07:00 to 20:30 then off
    If sw1 open then off

    That should accomplish the task right?

    Sent from my ADR6350 using Tapatalk 2

  8. #8
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,495

    Can someone check my code?

    Quote Originally Posted by Railcar79 View Post
    I tried aqualifters (3 different on a JBJ ATO) and they were by far the worst most useless pumps I have ever run since I started salt 25 years ago. I would rather hand dose than use them. But I guess I will just go with this code

    Fallback off
    If time 07:00 to 20:30 then off
    If sw1 open then off

    That should accomplish the task right?

    Sent from my ADR6350 using Tapatalk 2


    That will not work. There is nothing to turn on the outlet.

    This is a very basic nighttime-only ATO program with debouncing of the switch and a high pH shutoff.

    Fallback OFF
    Set OFF
    If Swi1 CLOSED Then ON
    If Time 07:00 to 20:30 then OFF
    If pH > 8.30 Then OFF
    Defer 000:30 Then ON
    Defer 000:10 Then OFF
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  9. #9
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,495

    Can someone check my code?

    I have to agree with you about Aqualifters. I've had nothing but problems with them.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  10. #10
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    Ok. Thank you Russ, I am still figuring coding out. Some days my old timers and float swiches seem so much easier. One of these days, I will figure out feed timers...lol

    Sent from my ADR6350 using Tapatalk 2

  11. #11
    Frequent Visitor LobsterOfJustice's Avatar
    Join Date
    Jun 2013
    Location
    Cary, NC
    Posts
    859
    Quote Originally Posted by RussM View Post
    That will not work. There is nothing to turn on the outlet. This is a very basic nighttime-only ATO program with debouncing of the switch and a high pH shutoff. Fallback OFFSet OFFIf Swi1 CLOSED Then ONIf Time 07:00 to 20:30 then OFFIf pH > 8.30 Then OFFDefer 000:30 Then ONDefer 000:10 Then OFF
    Technically, yes this will work, but you are going to end up with a lot of kalk being dumped in at 20:30 after having no top-off all day. I would make it OSC-based with a switch over-ride (as opposed to switch-activated).
    180g reef with all the bells and whistles

  12. #12
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    I took my standard code last night and manually shut off the ATO system all day and only let it run at night. on the 3 day graph it looks MUCH better, that is why I am looking at only allowing it to run at night.

    72 hr graph.jpg

  13. #13
    Frequent Visitor LobsterOfJustice's Avatar
    Join Date
    Jun 2013
    Location
    Cary, NC
    Posts
    859
    When you let it run normally (all day) about how often does it turn on, and for how long?
    180g reef with all the bells and whistles

  14. #14
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    this is the best I can do for you there. I work away from home and I dont get alot of time to observe the systems functioning.
    ato chart.jpg

  15. #15
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    from what I can see anywhere from 5-15 seconds 21 times yesterday

  16. #16
    Frequent Visitor LobsterOfJustice's Avatar
    Join Date
    Jun 2013
    Location
    Cary, NC
    Posts
    859
    Is that over the whole 24 hours or just overnight, with no topoff during the day?
    180g reef with all the bells and whistles

  17. #17
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    That graph was for the 2 days before going to nighttime only

    Sent from my ADR6350 using Tapatalk 2

  18. #18
    Frequent Visitor LobsterOfJustice's Avatar
    Join Date
    Jun 2013
    Location
    Cary, NC
    Posts
    859
    Looks like its basically coming on every hour. To avoid kalk overdose once the ATO is allowed, I would run it as an OSC statement, with a float switch and if time over-ride. Something like "Fallback OFF", "OSC 000:00/000:10/029:50 then ON", "If Sw1 OPEN then OFF", "If Time 07:00 to 20:30 then OFF". This will allow the ATO pump to run 10 seconds every 30 minutes, EXCEPT if the float switch says the sump is full, and EXCEPT during the daytime. Hope that makes sense. You will have to keep a close eye on it for a few days, you might need to adjust the OSC statement up/down depending on your needs. I really can't recommend float-activated kalk dosing... theres so much that could go wrong, its just too dangerous.
    180g reef with all the bells and whistles

  19. #19
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    Unfortunately it is my only option for now, and using float based dosing, the tank has ran great for a couple years, just trying to smooth the curve a bit

    Sent from my ADR6350 using Tapatalk 2

  20. #20
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by LobsterOfJustice View Post
    Looks like its basically coming on every hour. To avoid kalk overdose once the ATO is allowed, I would run it as an OSC statement, with a float switch and if time over-ride. Something like "Fallback OFF", "OSC 000:00/000:10/029:50 then ON", "If Sw1 OPEN then OFF", "If Time 07:00 to 20:30 then OFF". This will allow the ATO pump to run 10 seconds every 30 minutes, EXCEPT if the float switch says the sump is full, and EXCEPT during the daytime. Hope that makes sense. You will have to keep a close eye on it for a few days, you might need to adjust the OSC statement up/down depending on your needs. I really can't recommend float-activated kalk dosing... theres so much that could go wrong, its just too dangerous.
    +1 I have a how to guide on this topic that Russ is reviewing and will be released soon after. Ill link it when its open to everyone.

    Anyone who cannot cope with mathematics is not fully human. At best he is a tolerable subhuman who has learned to wear shoes, bathe and not make messes in the house. -robert heinlein

  21. #21
    Frequent Visitor LobsterOfJustice's Avatar
    Join Date
    Jun 2013
    Location
    Cary, NC
    Posts
    859
    Quote Originally Posted by Railcar79 View Post
    Unfortunately it is my only option for now, and using float based dosing, the tank has ran great for a couple years, just trying to smooth the curve a bitSent from my ADR6350 using Tapatalk 2
    What is the code you have been using for the past few years?
    180g reef with all the bells and whistles

  22. #22
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    Last few years I used a JBJ ATO. I finally caved and got my 2nd controller (first one was a huge mistake). I know the apex can do a lot, I just can't seem to tell it what I want it to do and have it work.

    Sent from my ADR6350 using Tapatalk 2

  23. #23
    Frequent Visitor LobsterOfJustice's Avatar
    Join Date
    Jun 2013
    Location
    Cary, NC
    Posts
    859
    My code above should give you a safe way of doing what you are looking for, you just might have to adjust the times to suit your needs. You wouldn't be able to simply take something like the JBJ and put it on a timer, because when the timer activates it, it's going to make up 12 hours worth of evap with kalk all at once which is way too much. That's why I changed the code to OSC based.
    180g reef with all the bells and whistles

  24. #24
    Frequent Visitor
    Join Date
    Feb 2014
    Location
    United States
    Posts
    52
    So If I were to go with a dosing every 6 hours (to cut down on kalk getting dumped in all at once) would this be better?

    Fallback OFF
    Set OFF
    If Sw1 CLOSED Then ON
    OSC 0:00/5:00/355:00 Then OFF
    If pH > 8.30 Then OFF
    Defer 000:30 Then ON
    Defer 000:10 Then OFF

  25. #25
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,495
    That won't work. OSC has hard on and off states, so it will ALWAYS override any statement(s) listed above it. Also, your OSC... Then OFF does not make sense for this application - you have it programmed to be OFF for 5 minutes and ON for 355.

    Fallback OFF
    OSC 0:00/5:00/355:00 Then ON
    If Sw1 OPEN Then OFF
    If pH > 8.30 Then OFF
    Defer 000:30 Then ON
    Defer 000:10 Then OFF

    Now, the OSC will try to turn on the outlet for 5 minutes every 6 hours. But that will only happen if the switch is open (ATO is needed). If the switch is closed, then nothing will happen. If the switch is open when the OSC turns on the outlet, and then the switch goes closed as top-off kalk/water gets, the outlet will shut off - so, only enough will be added to raise the switch.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

Page 1 of 2 12 LastLast

Similar Threads

  1. Please Check My First OSC Code
    By Rshashaty in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 2
    Last Post: 04-15-2020, 16:47
  2. Help! Check my code!
    By jstross94 in forum Misc Apex Usage & Programming
    Replies: 2
    Last Post: 07-28-2019, 18:05
  3. Please check my code...
    By alexkharden in forum Misc Apex Usage & Programming
    Replies: 4
    Last Post: 02-22-2016, 11:54
  4. Email code check....
    By Evilbass in forum Networking & Internet Connectivity
    Replies: 2
    Last Post: 03-25-2015, 05:49
  5. Skimmer Code Check
    By fmjets11 in forum Misc Apex Usage & Programming
    Replies: 1
    Last Post: 03-19-2014, 09:31

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •