Thread: New Apex Jr. temp probe issue

  1. #1
    Regular Vistor
    Join Date
    Jan 2013
    Location
    US, Pacific Time
    Posts
    18

    New Apex Jr. temp probe issue

    I've been running a new Apex Jr. without issue for about a month on a QT tub with just an LED light and a heater. I moved the Apex Jr to a reef tank, plugged it into a different wall outlet and now the temp probe is bouncing around between 78.1-78.5 and back down. I have a MH light, heater, and fan set up on the Apex Jr., all basic programs. I added the fan when I moved the Apex to the tank. It wont stay settled on a temp, just goes 78.1-78.3-78.4-78.5-78.4-78.3 and so on and so forth. I have unplugged the system form the wall outlet, let it sit for a few minutes and plugged back in. It comes on and settles just fine like its working well, within 10 or so minutes the temp starts bouncing between back and forth as described above. Any thoughts on what might be the problem?

  2. #2
    Master Control Freak aquamanic's Avatar
    Join Date
    Jan 2013
    Location
    Baton Rouge, LA
    Posts
    6,181
    Turn off all your outlets.

    See if the temp stabilizes over the course of 30 minutes.

    If it's stable with no outlets turned ON, something is causing it t be erratic..just need to figure out what.

    Turn on one outlet, doesn't matter which one

    See if there's an impact to your temp probe. Repeat the process.
    Al

    I do not work for Neptune. Please do not send me PMs with technical questions or requesting assistance - use the forums!
    For Neptune support send an email (don't call) to: [email protected] .
    Manuals for all products including the
    Comprehensive Reference Manual can be found here.

  3. #3
    Regular Vistor
    Join Date
    Jan 2013
    Location
    US, Pacific Time
    Posts
    18
    By "off" do you mean each outlet is in the off position in their programming? Or do you mean wipe the program completely so there is no code?

  4. #4
    Master Control Freak aquamanic's Avatar
    Join Date
    Jan 2013
    Location
    Baton Rouge, LA
    Posts
    6,181
    Just turn them OFF. You want to see if any devices are causing the problem so you're going to turn them on one by one.
    Al

    I do not work for Neptune. Please do not send me PMs with technical questions or requesting assistance - use the forums!
    For Neptune support send an email (don't call) to: [email protected] .
    Manuals for all products including the
    Comprehensive Reference Manual can be found here.

Similar Threads

  1. Help! New temp probe issue...
    By SUS in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 1
    Last Post: 02-18-2022, 14:45
  2. Replies: 2
    Last Post: 08-15-2019, 08:05
  3. Question: Temp Probe Issue
    By sun1914 in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 2
    Last Post: 11-26-2015, 19:57
  4. Temp probe issue
    By umax5555 in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 3
    Last Post: 04-28-2015, 13:42
  5. Question: Temp probe of Apex module and temp probe of PM2 (salinity) give different readings
    By Klaas Oreel in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 2
    Last Post: 08-03-2013, 17:06

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •