I am a long-time owner of Neptune Systems' products, and have been helping fellow controller owners in various Internet forums for many years. Some of you may have noticed that I spend A LOT of time doing so :)
In all those years, I've seen patterns of things that people sometimes do which they shouldn't, and things that people don't do which they should. For quite some time, I've been planning to put together a collection of miscellaneous brief informational "nuggets" intended to help new Apex owners avoid making some of these common mistakes, to debunk some common misconceptions, and to avoid some pitfalls.
Here it is...
In some cases, I may be rather blunt, but I assure you that it's just to emphasize a certain point ;)
New APEX Users: Read This Thread!
CONDUCTIVITY PROBES
There are four common misconceptions about calibration of a PM2 (or conductivity port in the new 2016 Apex) and a Neptune Systems conductivity probe.
- There is bogus info about calibration of a conductivity probe out there on Internet forums where other controller users have written that when the 1st step of the calibration process is performed, the conductivity probe should be completely dry, and that "dry" means to let it sit out of water for several hours or even overnight. This is wrong! Just follow the procedure in the PM2 manual.
The calibration procedure in the
PM2 manual, which says:
Quote:
Apex Display: Go to Setup –> Cond Setup –> Cond Calibrate
1. If you have more than one Conductivity probe enabled on your system, use the up/down arrow keys to choose the probe you wish to calibrate, press Select.
2. Remove the conductivity probe from the tank and rinse with RO/DI water, then dry it off. It is not necessary to let the probe dry out – just gently shake off excess water and blot the tip with the corner of a paper towel.{remainder of procedure omitted}
- A myth that has been perpetuated in forums for years that a new Neptune Systems conductivity probe must be soaked in tank water for an extended period of time of a week or more before calibrating for the first time.
A new (or dried out) conductivity probe need only be soaked for a few hours to a day prior to calibration.
- Refractometer calibration fluids and conductivity calibration solutions are not the same. Use the proper calibration solution.
In general, you cannot use calibration solution meant for calibrating a saltwater refractometer to calibrate a conductivity probe (and vice versa). While there are a couple of calibration solutions available which are labeled as being suitable for both uses, I've found the results of using them to be inconsistent. I strongly recommend that only the Neptune 53mS (53,000μS) calibration solution be used to calibrate a Neptune conductivity probe. It has always given me good results.
- Do not expect a conductivity probe and a refractometer to give the exact same salinity reading.
Conductivity/salinity probes estimate salinity by measuring the electrical conductivity of a liquid. Refractometers estimate salinity by measuring how much light bends as it passed through the liquid sample - a physical property. Both are indirect methods of measuring salinity, and different measurement methods can give different results. Measurements obtained by a properly-calibrated conductivity probe and a properly-calibrated refractometer should be close, but will not necessarily be exactly the same. Plus, refractometers are subject to reading errors due to parallax.... if you are not looking dead center down the body of some refractometers, the refractometer may show a different reading compared to when properly centered with your eye.
APEX FUSION - WHAT IT IS and WHAT IT ISN'T
APEX Fusion is the primary user interface for management and monitoring of your Apex system and your aquarium. Apex Fusion lives "in the cloud", out there on the Internet. It does not reside in the Apex itself.
Some key points:
- You cannot install APEX Fusion on the Apex or on your computer - it is a web site you access with a web browser like Firebox or Safari, just like you access www.cnn.com, www.espn.com, www.google.com, etc.
- The software which runs inside the Apex is called "Apex Operating Systems" (AOS) for Apex (2016) models and "firmware" for Apex Classic models.
- AOS and Apex Classic firmware is not APEX Fusion.
- When you update Apex firmware, you are not updating APEX Fusion.
- You cannot update APEX Fusion. APEX Fusion is updated as necessary by Neptune Systems' Fusion development team. Updates to APEX Fusion are transparent to you - you don't need to do anything to get or use them.
- The Apex Classic Dashboard consists of the web pages which are in the Apex itself. The Classic Dashboard is the original Apex user interface which existed long before before the advent of APEX Fusion. It's still available in the Apex, but the Classic Dashboard is not APEX Fusion. Note: The Classic Dashboard is present only in the Apex Classic/Gold, Apex Lite, and Apex Jr. It is not in the new 2016 model of Apex. The 2016 Apex has a totally new and different local user interface called APEX Local.
- Your Apex's programming does not run in APEX Fusion; it runs inside the Apex.
- When you program your Apex using the APEX Fusion user interface, that programming is sent to and stored in the Apex itself.
- If your Apex loses communications with APEX Fusion, programming will still continue to be executed.
When posting here in the Neptune Systems Community Forum, please do not use the term "APEX Fusion" as a collective term for the entire Apex software & user interface ecosystem... that just causes confusion.
Also, use the APEX Fusion sub-forum here only for posts which DIRECTLY pertain to using the Apex Fusion web site. Use the other sub-forums as most appropriate for the topic of your programming related questions, your firmware questions, etc.
New APEX Users: Read This Thread!
Understanding the Set command
The Set command is the simplest command used in the Apex, but it is sometimes misused. It is used to define the default state of an outlet whenever no other program statement is true.
One thing I see commonly is confusion between the Set and Fallback statements. They are not equivalent and are not interchangeable. Fallback is a special command that has no affect on the state of an outlet during normal program execution - Fallback tells a module what to do should that module lose communications with the Apex. See this sticky post for more about Fallback.
Now, let's review proper usage of Set:
The Set requires an action to be specified - OFF, ON, or if the output being programmed supports variable intensity, a % value or a profile name.
- Set OFF
- Set ON
- Set 75
- Set Constant50
The Set statement, if used, should be used to configure the normal, default state of an output. In general, if an output should be off most of the time or under normal conditions, then a Set OFF should be used. If an output is needed to be on all or most of the time, except when certain conditions are met, then using Set ON is appropriate. In summary, use Set to assign the normal state, then use additional programming for exceptions.
These two programs do almost exactly the same thing - make an output be on for 10 hours, from 8AM to 6PM But one is the "right" way, the other is the "wrong" way.
RECOMMENDED
Set OFF
If Time 08:00 to 18:00 Then ON
NOT RECOMMENDED
Set ON
If Time 18:00 to 08:00 Then OFF
The first one is logical, and easier to understand. The second one uses a sort of backwards logic, and is not as easy to understand.
Let's look at a simple program for a lighting schedule:
Set OFF
If Time 08:00 to 17:59 Then ON
Whenever the If Time statement is true (between 08:00 and 18:00, the outlet will be ON. Whenever the If Time statement is not true, the Set OFF statement tells the outlet to be OFF. Simple enough.
I sometimes see people do this instead:
If Time 08:00 to 17:59 Then ON
If Time 18:00 to 07:59 Then OFF
So what's the difference between the first example I gave (using one Set and one If Time statements) and this one (using two If Time statements)? Functionally, the outcome is exactly the same - the outlet will be on from 8AM to 6PM, and off the rest of the day. But the first program is better, and the preferred method - it's cleaner, more efficient programming. Plus, if you need to modify the ON time, you only need to modify one statement, not two statements.
Side note: Are you wondering why I used 17:59 instead of 18:00 in the statements above? See the USING THE IF TIME STATEMENT post in this thread.
In general, you should use a Set and a conditional (If) statement whenever you can, instead of using two conditional statements.
But there are four occasions when a Set statement must not be used:
1. Never add a Set ON or Set OFF into programming which was created using a Vortech, Radion, variable, WAV, SKY, Sol, Hydra/Vega, Prime/Hydra HD, or COR scheduler wizard.
2. Never use a Set ON or Set OFF in the same program as an OSC command. A Set statement is not needed because the OSC command has explicit ON and OFF states.
3. Never use a Set On or Set OFF when it is desired to operate over a range of probe values, such as if using temperature to control a heater.
Let's take an example: we want to have an outlet used for a heater come ON if the temp drops below 77.0 degrees, and stay on until the temp exceeds 78.0 degrees.
Wrong:
Set OFF
If Temp < 77.1 Then ON
If Temp > 77.9 Then OFF
The problem with this program is that it will not cause the outlet to operate over the desired range of temperature; instead, it will operate around a single temp of 77.0 degrees. If the temp drops to 77.0, the heater outlet will turn ON, and it will shut off as soon as the temp goes up to 77.1. The If Temp > 79.9 statement does absolutely nothing here, because the Set OFF will be the only true statement as soon as the temp goes up to 77.0. The result will be that your heater gets switched on and off fairly rapidly. But that's not what we want... we want it to stay on until the temp is raised to 78.
Right:
If Temp < 77.1 Then ON
If Temp > 77.9 Then OFF
In this second simple program, we did not include a Set statement. The outlet will turn ON as soon as the temperature drops below 77.1. It will then stay ON until the temp hits 78.0, and then will turn OFF. It will then stay OFF until the temp goes below 77.1 again, then will turn ON, stay on until the temp once again exceeds 77.9, so on and so forth. This will maintain the tank temperature with the specified 1-degree range.
In summary:
A program with a Set and one If statement will operate around a single threshold.
A program with two If statements testing for low and high values of the same input will operate over a range - i.e., between the two specified thresholds.
Do not mix the two techniques.
4. Never use a Set On or Set OFF when using two switch inputs or LLS values to control an outlet, such as if using a low and high switch to control refilling of an ATO reservoir.
Wrong:
Set OFF
If ResLo CLOSED Then ON
If ResHi Open Then OFF
Right:
If ResLo CLOSED Then ON
If ResHi OPEN Then OFF
One more point about using Set... always use a Set and *one* If statement when testing for the state of a single switch input rather then using two If statements to check for both CLOSED and OPEN states of the same switch input.
This is wrong:
Set OFF
If Switch CLOSED Then ON
If Switch OPEN Then OFF
In this case, the If Switch OPEN Then OFF line is not needed - the Set OFF statement handles turning the outlet OFF whenever the If Switch CLOSED Then ON line is not true. Some people mistakenly think that this will add redundancy - it will not.
This will work, but is not the right way:
If Switch CLOSED Then ON
If Switch OPEN Then OFF
This is the right way:
Set OFF
If Switch CLOSED Then ON
One final note... The OSC (oscillate) command is used to turn an output ON and OFF at regular intervals. OSC has explicit ON and OFF states, so a Set ON or Set OFF statement is not needed and should never be used in any output program containing an OSC statement.
Wrong:
Set OFF
OSC 0:00/5:00/5:00 Then ON
Right:
OSC 0:00/5:00/5:00 Then ON