    DC8 Output 2 is not turning off !!

    Hi, I have an old AC3 working very nice, but the output 2 of my 2nd DC8 looks to do not respond.
    I configured this:
    If FeedB 040 Then RTN OFF
    If FeedB 040 Then SKM OFF
    If FeedB 040 Then WV1 OFF
    If FeedB 040 Then WV2 OFF
    If FeedB 040 Then WV3 OFF
    If FeedB 040 Then WV4 OFF
    If FeedB 040 Then WV5 OFF
    If FeedB 040 Then WV6 OFF

    Where Output2 od 2nd DC8 is used as SKM.
    If I select FeedB, all turns off except SKM.
    SKM is ON all the time.
    What can I do? In my first DC8, Output 2 is not usable.

    I remember I saw saomething about outoput 2 on DC8, but can remember what.
    Thanks in advance for your help.

  2. #2
    NSI Member
    Join Date
    Jan 2016
    Location
    Vineland, NJ
    Posts
    386
    Please post the code for outlet 2 on the DC8.

  3. #3
    Frequent Visitor
    Join Date
    Jul 2014
    Location
    Mexico
    Posts
    113
    This is the only line:
    If Time > 00:00 Then SKM ON

    Return pump has the same line and it is working.

  4. #4
    NSI Member
    Join Date
    Jan 2016
    Location
    Vineland, NJ
    Posts
    386
    Is there a reason you are using an If Time statement instead of Set ON?

    Also, what skimmer are you using? It is possible that it may not be drawing enough current for the TRIAC to shut it off.

  5. #5
    Frequent Visitor
    Join Date
    Jul 2014
    Location
    Mexico
    Posts
    113
    Dont know about Set on. It is a beckett skimmer. A reeflo swordtail pump.

  6. #6
    NSI Member
    Join Date
    Jan 2016
    Location
    Vineland, NJ
    Posts
    386
    Can you turn the outlet off manually using either Fusion or the display?

    What is the power rating of the pump you are using? Check out this sticky to see if you may be having this problem.
    https://forum.neptunesystems.com/sho...rs-and-outlets

  7. #7
    Frequent Visitor
    Join Date
    Jul 2014
    Location
    Mexico
    Posts
    113
    Does this apply to DC8 also? Mine is not EB8

  8. #8
    NSI Member
    Join Date
    Jan 2016
    Location
    Vineland, NJ
    Posts
    386
    I believe so. If I remember correctly, outlets 4 and 8 have a "Relay" designation indicating a mechanical relay.

  9. #9
    Frequent Visitor
    Join Date
    Jul 2014
    Location
    Mexico
    Posts
    113
    You are correct. But I do not know if there is something different about outlet 2.

Similar Threads

  1. Help! Turning Gyre pumps with the DC8 is not working on time
    By Reef Man in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 5
    Last Post: 10-26-2020, 12:49
  2. Help! Turning on a float switch and turning off after time elapsed help
    By sfox365 in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 2
    Last Post: 05-21-2019, 11:35
  3. Help! Cor20 output decreased after turning off
    By nbd13 in forum COR-15 & COR-20 Pumps
    Replies: 2
    Last Post: 04-09-2019, 15:49
  4. Question: Kessil A160WE turning on after and turning off before the scheduled time?
    By Tonii87 in forum Apex Programming for Lighting
    Replies: 5
    Last Post: 05-04-2018, 07:59
  5. Help! 24 volt output from FMM not turning off
    By jonathan9573 in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 6
    Last Post: 03-04-2018, 16:16

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •