    Will the Energy Bar 4 handle my 72" Cebu Sun Fixture?

    Just like the title says, Will the Energy Bar 4 handle my 72" Cebu Sun Fixture?
    It has 3 250Watt metal halides and 4 80 watt t5s
    I would love to use it to control the lights but I am worried they pull to many amps

  2. #2
    Classic User
    Join Date
    Sep 2015
    Location
    Alexandria, Virginia 22311
    Posts
    753
    Depending on what else is plugged into your EB4 the answer is that it can handle this fixture.

    Each outlet can handle 8 amps. Outlet 3 can actually handle 12 amps by itself. But the total EB4 current draw must not exceed 15 amps total.

    That said, it is not a good practice to load up an outlet strip or an energy bar all the way up to its rated limits. Rather, a good practice is to stay below about 75-80% of the max rated current. That works out to staying
    below 6-6.5 amps on the individual outlets (1,2,4) and
    below 10 amps on outlet 3 and
    below 11.5-12 amps for the entire EB4 current draw.

    Since your fixture only draws about 9 amps which is above the 6-6.5 amp good practice limit on outlets 1, 2, 3 but below 10 amps for outlet 3, you should be able to operate it on outlet 3 as long, as other devices on outlets 1,2 and 3 are not tipping you over the total EB4 amperage rating of 15 amps - in fact preferably staying below its good practice limit of 11.5-12 amps total.

    fab

  3. #3
    New User
    Join Date
    Jul 2016
    Location
    central
    Posts
    2
    I plan on running the halides on one outlet and the t5s on another. I should be ok as the other outlets will be for heater and return pump for now

  4. #4
    Classic User
    Join Date
    Sep 2015
    Location
    Alexandria, Virginia 22311
    Posts
    753
    It is all about amps per outlet and total amps for the EB4. Do the math. Then you can proceed with confidence. This can be a safety issue so do be thorough in your analysis.

Similar Threads

  1. Question: Plugging in Energy Bar into another Energy Bar outlet.
    By wyattray in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 7
    Last Post: 11-29-2017, 23:10
  2. "Reverse" Sun Command Help Please
    By LHillman in forum Misc Apex Usage & Programming
    Replies: 0
    Last Post: 09-07-2017, 06:35
  3. Question: Connecting base, energy bar 832 and add-on Energy Bar 4
    By faulk28 in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 1
    Last Post: 02-05-2017, 09:52
  4. Help! Energy Bar "Device" on fusion
    By bebenson in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 3
    Last Post: 07-12-2016, 16:21
  5. Ramp time on my Kessil not working properly when using "if sun"
    By Phisher13 in forum Apex Programming for Lighting
    Replies: 4
    Last Post: 07-09-2014, 12:10

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •