Thread: EB832 not reporting Amps or Watts at times and undervoltage

  1. #26
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    What error are you referring too? I see no error in your screenshot. However, I do see one thing that you might have done incorrectly... you used a telnet command of 'eb8zero 1'. The syntax of the command is 'eb8zero #' where # is the Aquabus address of the EnergyBar of interest. It's unlikely that your EnergyBar is at Aquabus address 1; Address 1 is normally reserved for a display module. Typically, the first EB832 connected to an Apex or Apex EL is at address 2. Use the left-most column of the Modules List in APEX Fusion to positively identify the address of the desired EnergyBar.


    BTW, it is poor forum behavior to bump a thread barely a half hour after you posted. Please show some patience.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  2. #27
    New User
    Join Date
    Mar 2022
    Location
    chicago CDST
    Posts
    5
    Thank you and sorry for the lack of etiquette. I will attempt it again tonight using the 3. Please review the picture to confirm it’s accurate
    Attached Images Attached Images

  3. #28
    New User
    Join Date
    Mar 2022
    Location
    chicago CDST
    Posts
    5
    Quote Originally Posted by Themoth View Post
    Thank you and sorry for the lack of etiquette. I will attempt it again tonight using the 3. Please review the picture to confirm it’s accurate
    thank you anyway Fam, Going to the Neptune Professionals with a call on Monday to resolve this issues. I report back so others will be helped!

  4. #29
    New User
    Join Date
    Mar 2022
    Location
    chicago CDST
    Posts
    5
    Quote Originally Posted by Themoth View Post
    thank you anyway Fam, Going to the Neptune Professionals with a call on Monday to resolve this issues. I report back so others will be helped!
    NEPTUNE determined its a faulty power bar and they are replacing it.

  5. #30
    New User
    Join Date
    Mar 2022
    Location
    Texas
    Posts
    4
    Hey Neptune family. I'm having trouble with this. I was finally able to use my Mac to get the original command to open, but I never saw a place to login or to access anything from there. I tried just posting the eb8zero 2 command, but it just stated command not found. Any help would be appreciated. Thank you.

    Dustin

  6. #31
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    Dustin, it sounds like you only opened Terminal but did not issue the nc command as described elsewhere in this thread.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  7. #32
    New User
    Join Date
    Mar 2022
    Location
    Texas
    Posts
    4
    Quote Originally Posted by RussM View Post
    Dustin, it sounds like you only opened Terminal but did not issue the nc command as described elsewhere in this thread.
    I believe I did. I did this below version. It then popped up several lines of things about the apex, but that’s where I then wasn’t sure how to proceed.

    nc -c 192.168.1.50 23

  8. #33
    New User
    Join Date
    Mar 2022
    Location
    Texas
    Posts
    4
    Quote Originally Posted by RussM View Post
    Dustin, it sounds like you only opened Terminal but did not issue the nc command as described elsewhere in this thread.
    This is what I get when completing the original command. Any help would be appreciated. Thank you.

    Screen Shot 2022-03-20 at 8.59.51 PM.png

  9. #34
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    You did not follow the examples given. The number 23 must be specified in the nc command as shown
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  10. #35
    New User
    Join Date
    Mar 2022
    Location
    Texas
    Posts
    4
    Quote Originally Posted by RussM View Post
    You did not follow the examples given. The number 23 must be specified in the nc command as shown
    Thanks for the help. I did miss the "23" at the end. I was able to get it reset and is now working properly.

    D

  11. #36
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    Quote Originally Posted by dcwosbee View Post
    Thanks for the help. I did miss the "23" at the end. I was able to get it reset and is now working properly.

    D
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  12. #37
    Frequent Visitor
    Join Date
    Sep 2018
    Location
    US, EST
    Posts
    72
    Quote Originally Posted by RussM View Post
    Hi Russ,

    Is there a way to calibrate EB832 voltage readings via telnet? I have one that is reading 10v higher than the others, and confirmed this with a multimeter. I performed the amperage calibration.

  13. #38
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    Quote Originally Posted by TheHarold View Post
    Hi Russ,

    Is there a way to calibrate EB832 voltage readings via telnet? I have one that is reading 10v higher than the others, and confirmed this with a multimeter. I performed the amperage calibration.
    There is not.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Watts and Amps all 0
    By ddrueckh in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 16
    Last Post: 04-27-2023, 19:05
  2. Help! Watts / Amps
    By damontoy in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 0
    Last Post: 05-29-2019, 17:21
  3. Volts, Amps, Watts displayed how accruate?
    By p7willm in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 9
    Last Post: 08-13-2016, 17:14
  4. EB8 reporting 0 amps 4.32_7A14
    By shellcode in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 2
    Last Post: 08-19-2014, 04:54
  5. Amps per watts
    By Tab28 in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 14
    Last Post: 03-23-2014, 13:58

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •