    All dead now what

    I came home and both aquariums were totally off, everything. I plugged the pumps and lights straight into the wall. Now how do I figure out what needs replacing. The apex control module or the power strip?


    Sent from my iPhone using Tapatalk

  2. #2
    Frequent Visitor
    Join Date
    Mar 2014
    Location
    Orlando
    Posts
    59
    The only bit of any power on the entire system is a faint green status light slowly fading on and off on the power strip.


    Sent from my iPhone using Tapatalk

  3. #3
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,489
    I've not heard of a EnergyBar status light slowly fading on and off. They may blink on and off. Disconnect the Apex base - does that change in any way? If not, then the EB is suspect.

    See if you have a 12vdc adapter you could try to power up the Apex base. Many router's and modems use a compatible power supply. It must be 12VDC & 500ma or higher.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  4. #4
    Frequent Visitor
    Join Date
    Mar 2014
    Location
    Orlando
    Posts
    59
    Now that it is completely dark. Fading may have been incorrect. It is blinking about ever second. A constant blink.

    I unplugged the module from the power strip. It did nothing. So if i plug the adapter into the power slot of the module and it lights green. Does that mean it is the power strip?


    Sent from my iPhone using Tapatalk

  5. #5
    Frequent Visitor
    Join Date
    Mar 2014
    Location
    Orlando
    Posts
    59
    Will a 12v 2A adapter work. Not sure what 500ma is.


    Sent from my iPhone using Tapatalk

  6. #6
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,489
    Yes it will. "ma" is milliamperes.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  7. #7
    Frequent Visitor
    Join Date
    Mar 2014
    Location
    Orlando
    Posts
    59
    The module powers on and turns on display screen and ph/ temp probes. So i am guessing it is safe to say it is the power strip.

    If i replace the 8 power strip. Will i have to re-program all the outlets? Is there any way to get module to think the new is the old?


    Sent from my iPhone using Tapatalk

Similar Threads

  1. I think its finally dead :(
    By Darcy in forum Networking & Internet Connectivity
    Replies: 4
    Last Post: 10-19-2017, 22:53
  2. Apex dead?
    By thegreatga in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 1
    Last Post: 07-22-2017, 06:31
  3. Is my Dos dead?
    By Maximus in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 3
    Last Post: 01-21-2015, 08:26
  4. LSM dead
    By TWS in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 6
    Last Post: 01-06-2015, 06:11
  5. Help! Apex went dead
    By jschwab45212 in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 10
    Last Post: 12-11-2014, 21:45

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •