Results 1 to 7 of 7

Thread: Salinity Probe drops BIG TIME When Temp Goes Up

  1. #1
    Frequent Visitor
    Join Date
    Jul 2013
    Location
    NJ
    Posts
    213

    Salinity Probe drops BIG TIME When Temp Goes Up

    I know salinity is closely related to the temperature however now that summer is here my tank temperature during the day goes from normal 77.5 to around 2 degrees higher by later in the day and when the temperature goes up just the two degrees my salinity probe drops from 35ppm down to 33.5! Then during the night as the temperature drops the salinity goes back up to normal.

    The biggest issue is that when the reading drops that low I keep getting email alarms warning me of the low salinity even though in reality it's still around the normal 35.

    Is there anything that I can do to stop getting the email alarms without of course deleting the alarm code?

    AND is this normal for the salinity probe drop THAT much on just two degrees?

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    That sounds about right actually. Measured conductivity varies roughly 2 ppt per degree Celcius if you do not enable temp compensation (varies a bit depending on which study you look at and what the relative concentration of NaCl vs other elements)

    Enable temp compensation and you won't have this problem (or will at least minimize it to like 0.1 or 0.2 change vs the 1.5 you are getting now).

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    Frequent Visitor
    Join Date
    Jul 2013
    Location
    NJ
    Posts
    213
    I do have temp compensation enabled at 2.2!

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Can you post your cond graph overlayed with temp?

    You might be an engineer if...You have no life and can prove it mathematically.

  5. #5
    Frequent Visitor
    Join Date
    Jul 2013
    Location
    NJ
    Posts
    213
    Quote Originally Posted by zombie View Post
    Can you post your cond graph overlayed with temp?

    Screenshot_2017-06-20-19-43-07.jpg

    You might be an engineer if...You have no life and can prove it mathematically.
    Here you go

  6. #6
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Change the temp compensation to 1.1 as a start. My calculations show 0.6, but the problem could also be the firmware using 2.2ppt per degree F instead of C so try 1.1 first. If that doesn't even it out, Change to 0.6

    You might be an engineer if...You have no life and can prove it mathematically.

  7. #7
    Frequent Visitor
    Join Date
    Jul 2013
    Location
    NJ
    Posts
    213
    Quote Originally Posted by zombie View Post
    Change the temp compensation to 1.1 as a start. My calculations show 0.6, but the problem could also be the firmware using 2.2ppt per degree F instead of C so try 1.1 first. If that doesn't even it out, Change to 0.6

    You might be an engineer if...You have no life and can prove it mathematically.
    I changed it to the 1.1 and now reads 34.7 which I'll gladly take! Thanks so much for your help!

Similar Threads

  1. Replies: 2
    Last Post: 08-15-2019, 08:05
  2. Fusion, temp probe drops off display occasionally
    By Mjl714 in forum APEX Fusion
    Replies: 3
    Last Post: 03-08-2019, 17:03
  3. Salinity probe slowly drops to zero
    By Tuffloud1 in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 9
    Last Post: 03-02-2016, 02:05
  4. Conductivity Probe - Reading drops massively over time
    By johnnyenv in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 1
    Last Post: 09-04-2015, 09:32
  5. Temp Probe issue - randomly drops to 19.3
    By dark8nge1 in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 9
    Last Post: 03-02-2014, 18:02