    Flow Sensor with No Flow most of the time - OK?

    Is there any reason why I can't use a 1/4" flow sensor to monitor when my RO/DI is activated to add water to my sump? In other words, there would be no flow most of the time, but I want an email alarm when the flow starts going.

    I use Kalk for my topoff and will be adding the ATK soon to improve things and include some redundancy. The RO/DI connection is just one more redundancy to guard against the water level being too low, like my Kalk container needing to be refilled. I plan to set the level sensor lower than the Kalk low level sensor.

    Mickey

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,463

    Flow Sensor with No Flow most of the time - OK?

    The usable range of the FS-25 sensor is 3-12GPH. Most hobbyist-size RO/DI units do not output enough to meet the minimum spec of the sensor.

    So the answer to your question depends on the output flow rate of the RO unit.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    Frequent Visitor MickeyCT's Avatar
    Join Date
    Oct 2013
    Location
    Cheshire, CT
    Posts
    177
    Thanks, Russ. I forgot about that. I'll have to time how long it takes to fill a 45 gallon bucket with no other demands on the RO/DI system. Maybe a 5 gallon bucket would be easier.

    Mickey

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Unless your RODI has a dual membrane the flow will be too low. Typical is 75 GPD which is 3 gph. If you have a dual membrane it can be up to 150 GPD (6gph) which the sensor could read.

    You might be an engineer if...You have no life and can prove it mathematically.

Similar Threads

  1. Question: Return pump low flow alarm from FFM flow sensor
    By Cpage101 in forum APEX Fusion
    Replies: 3
    Last Post: 08-09-2019, 11:37
  2. Help! One of the of the two 1/2" FS-50 Flow Sensor on FLX_3 but the 2nd 1/2" flow Sensor will not display.
    By FoxTalbott in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 0
    Last Post: 12-26-2018, 04:03
  3. Optical sensor being confused as flow sensor?!
    By juanmanuelsanchez in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 8
    Last Post: 04-22-2018, 10:28
  4. Question: 1/4" Flow Sensor To Measure Top Off Water Then Turn On RO/DI Pump For Set Time
    By boomer2005uk in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 3
    Last Post: 08-13-2017, 08:36

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •