I am getting this alarm, any idea what that means?
FRM:Apex Fusion
SUBJ:Apex Fusion Alarm: apex1
MSGate: 2017-06-26 14:43:33 -0400
Status: OFF
Statement: Set OFF
I am getting this alarm, any idea what that means?
FRM:Apex Fusion
SUBJ:Apex Fusion Alarm: apex1
MSGate: 2017-06-26 14:43:33 -0400
Status: OFF
Statement: Set OFF
That means one of two things.
1. You have the email outlet in manual ON.
2. A previous alarm condition has cleared.
You might be an engineer if...You have no life and can prove it mathematically.
Manual is not on. As for clearing a previous alarm, don't have one and this one has continued for the last 2 hours
After further review, the clearing of a previous alarm may be the cause. Although the actual cause of the alarm Dos not seem to be shooting in the notifications. It wasn't noticed until I went into the alarm log.
Make sure you have a defer at the end of your email alarm code. Without the defer you can get the behavior you experienced because of transient spikes that don't actually mean something is wrong. These include switches bouncing, electrical interference in probes, quick pH changes from dosing too close to a probe, and air bubbles passing across a probe. A 30 second defer will eliminate these false readings.
You might be an engineer if...You have no life and can prove it mathematically.
I'm getting a Status: "On" Statement: "Set On" Error Email Alarm. I've deleted all the code, it still comes on. Added a defer statement, it still comes on. I'm at a loss on how to fix it.
This is my typical code, if one of these are throwing an alarm I get their statement, but if none of these are throwing an error I always get the "Set On" pinging me every hour.
If Tmp > 80.0 Then ON
If Tmp < 75.0 Then ON
If pH > 8.50 Then ON
If pH < 7.80 Then ON
If Error ATK Then ON
If ATK_HL CLOSED Then ON
Defer 400:00 Then ON
If ATO_LL OPEN Then ON
If FSK_HL CLOSED Then ON
Your email outlet needs to be in AUTO. Sounds like you have it in manual ON.
I also don't see Set OFF as your first line of code. That needs to be there.
You might be an engineer if...You have no life and can prove it mathematically.
Thanks zombie, looks like the Set OFF is what I was missing.
Do you really intend to have a 400 minute DEFER? That is nearly a 7 hour delay in getting a notification.
I do, when my skimmer shuts off in the evening it sets off the high level alarm.
There is a better way to do that.
Create a VO with the code
HighH2O (VO)
Set OFF
If ATK_HL CLOSED Then ON
If Outlet Return = OFF Then OFF
If Outlet Skimmer = OFF Then OFF
Defer 001:00 Then ON
Replace the ATK_HL line in your email with
If Outlet HighH2O = ON Then ON
And change the defer to like a minute or so in the email.
You might be an engineer if...You have no life and can prove it mathematically.
Thanks zombie! Entered the new code this evening and it works great.