    Getting the attached Non descript alarm

    I am getting this alarm, any idea what that means?

    FRM:Apex Fusion
    SUBJ:Apex Fusion Alarm: apex1
    MSGate: 2017-06-26 14:43:33 -0400
    Status: OFF
    Statement: Set OFF

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    That means one of two things.

    1. You have the email outlet in manual ON.

    2. A previous alarm condition has cleared.

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    Frequent Visitor
    Join Date
    Apr 2013
    Location
    Connecticut
    Posts
    164
    Manual is not on. As for clearing a previous alarm, don't have one and this one has continued for the last 2 hours

  4. #4
    Frequent Visitor
    Join Date
    Apr 2013
    Location
    Connecticut
    Posts
    164
    After further review, the clearing of a previous alarm may be the cause. Although the actual cause of the alarm Dos not seem to be shooting in the notifications. It wasn't noticed until I went into the alarm log.

  5. #5
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Make sure you have a defer at the end of your email alarm code. Without the defer you can get the behavior you experienced because of transient spikes that don't actually mean something is wrong. These include switches bouncing, electrical interference in probes, quick pH changes from dosing too close to a probe, and air bubbles passing across a probe. A 30 second defer will eliminate these false readings.

    You might be an engineer if...You have no life and can prove it mathematically.

  6. #6
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    Quote Originally Posted by zombie View Post
    That means one of two things.
    1. You have the email outlet in manual ON.
    If the alarm output was set to manual ON, the notification would be Status ON / Set OFF
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  7. #7
    New User
    Join Date
    Jan 2017
    Location
    Jupiter, FL
    Posts
    9
    I'm getting a Status: "On" Statement: "Set On" Error Email Alarm. I've deleted all the code, it still comes on. Added a defer statement, it still comes on. I'm at a loss on how to fix it.

    This is my typical code, if one of these are throwing an alarm I get their statement, but if none of these are throwing an error I always get the "Set On" pinging me every hour.

    If Tmp > 80.0 Then ON
    If Tmp < 75.0 Then ON
    If pH > 8.50 Then ON
    If pH < 7.80 Then ON
    If Error ATK Then ON
    If ATK_HL CLOSED Then ON
    Defer 400:00 Then ON
    If ATO_LL OPEN Then ON
    If FSK_HL CLOSED Then ON

  8. #8
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Your email outlet needs to be in AUTO. Sounds like you have it in manual ON.

    I also don't see Set OFF as your first line of code. That needs to be there.

    You might be an engineer if...You have no life and can prove it mathematically.

  9. #9
    New User
    Join Date
    Jan 2017
    Location
    Jupiter, FL
    Posts
    9
    Thanks zombie, looks like the Set OFF is what I was missing.

  10. #10
    Frequent Visitor Todd's Avatar
    Join Date
    Jan 2013
    Location
    Huntsville, AL
    Posts
    583
    Do you really intend to have a 400 minute DEFER? That is nearly a 7 hour delay in getting a notification.

  11. #11
    New User
    Join Date
    Jan 2017
    Location
    Jupiter, FL
    Posts
    9
    I do, when my skimmer shuts off in the evening it sets off the high level alarm.

  12. #12
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    There is a better way to do that.

    Create a VO with the code

    HighH2O (VO)
    Set OFF
    If ATK_HL CLOSED Then ON
    If Outlet Return = OFF Then OFF
    If Outlet Skimmer = OFF Then OFF
    Defer 001:00 Then ON

    Replace the ATK_HL line in your email with

    If Outlet HighH2O = ON Then ON

    And change the defer to like a minute or so in the email.

    You might be an engineer if...You have no life and can prove it mathematically.

  13. #13
    New User
    Join Date
    Jan 2017
    Location
    Jupiter, FL
    Posts
    9
    Thanks zombie! Entered the new code this evening and it works great.

  14. #14
    Regular Vistor
    Join Date
    Apr 2016
    Location
    Florida/Central
    Posts
    40
    Has your APEX been resetting/restarting randomly lately?


    Sent from my iPhone using Tapatalk

  15. #15
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Bif24701 View Post
    Has your APEX been resetting/restarting randomly lately?


    Sent from my iPhone using Tapatalk
    Totally wrong place to post this question. This is an old unrelated thread. To answer your question anyway there is a known bug that has been causing reboots for some users that is in some way related to network for the newest firmware version.

    You might be an engineer if...You have no life and can prove it mathematically.

  16. #16
    Regular Vistor
    Join Date
    Apr 2016
    Location
    Florida/Central
    Posts
    40
    Quote Originally Posted by zombie View Post
    Totally wrong place to post this question. This is an old unrelated thread. To answer your question anyway there is a known bug that has been causing reboots for some users that is in some way related to network for the newest firmware version.

    You might be an engineer if...You have no life and can prove it mathematically.
    I asked because I was getting the same notification each time mine reset. Didn’t see that it was older. Thanks for the info.


    Sent from my iPhone using Tapatalk

Similar Threads

  1. Did I set my kessil right? Screen shots attached.
    By reefco in forum Apex Programming for Lighting
    Replies: 2
    Last Post: 05-01-2016, 15:46
  2. Question: Could someone explain how a Profile is associated/attached to an Outlet
    By dbdisok in forum Apex Programming for Lighting
    Replies: 8
    Last Post: 03-05-2015, 05:24
  3. Attached first MP40W-ES but will not start
    By Phil in forum Apex Programming for Vortech, Tunze, & Other Controllable Pumps
    Replies: 10
    Last Post: 01-13-2015, 07:20
  4. Cant get Radion G2's attached to WXM
    By Tha Bizness in forum Apex Programming for Lighting
    Replies: 1
    Last Post: 04-01-2014, 07:32
  5. Temp probe attached to base unit and Temp probe attached to PM2 - should they be the same?
    By Fishytastic in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 10
    Last Post: 02-18-2014, 06:37

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •