Thread: How accurate is the current monitor on an EB8?

  1. #1
    Regular Vistor
    Join Date
    Apr 2017
    Location
    Boston, MA
    Posts
    26

    How accurate is the current monitor on an EB8?

    I just picked up another EB8. The first one I have has some tunze powerheads, algae reactor light, UV light, and fan. Nothing high output, in fact the only time it reads anything is when the fan is on. It gets to 0.3A.

    On the new (to me, I got it from a friend) one, I have nothing plugged into it and it is reading 0.5A. Granted, some outlets are turned on but there is no current flow so there shouldn't be reading anything. Is there a way to re-calibrate it with no load? apex2.jpg

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,463
    Yes, you can reset the zero on an EnergyBar. See page 139 in the Comprehensive Reference Manual. https://www.neptunesystems.com/support/docs/
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    Regular Vistor
    Join Date
    Apr 2017
    Location
    Boston, MA
    Posts
    26
    Quote Originally Posted by RussM View Post
    Yes, you can reset the zero on an EnergyBar. See page 139 in the Comprehensive Reference Manual. https://www.neptunesystems.com/support/docs/
    Is there any other way to do it? I tried turning on the telnet server on 3 different computers. I even pulled out my old Vista laptop and it doesn't work.

    Sent from my XT1585 using Tapatalk

  4. #4
    Regular Vistor
    Join Date
    Apr 2017
    Location
    Boston, MA
    Posts
    26
    And yes, I did activate the telnet server in Windows features

    Sent from my XT1585 using Tapatalk

  5. #5
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,463

    How accurate is the current monitor on an EB8?

    Quote Originally Posted by jasonrusso View Post
    Is there any other way to do it? I tried turning on the telnet server on 3 different computers. I even pulled out my old Vista laptop and it doesn't work.

    Sent from my XT1585 using Tapatalk
    You do not use a telnet server - you use a telnet client.

    Try this: https://www.chiark.greenend.org.uk/~...ty/latest.html Download puttyel.exe. No installation required - just download and run it.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  6. #6
    Regular Vistor
    Join Date
    Apr 2017
    Location
    Boston, MA
    Posts
    26
    After I wrote that last post I found my OLD Windows 98 laptop in the attic. After the 10 minute boot time (which we thought was fast) it worked. I knew there was a reason I was saving it!

Similar Threads

  1. Salinity probe in accurate
    By Jpbeen in forum Misc Apex Usage & Programming
    Replies: 2
    Last Post: 03-29-2021, 09:02
  2. EB8 not reading current correctly
    By jccaclimber in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 1
    Last Post: 09-30-2017, 13:34
  3. How accurate are these probes?
    By Scott.h in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 6
    Last Post: 12-21-2016, 10:06
  4. Question: EB8 current sensor
    By zombie in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 2
    Last Post: 04-12-2014, 08:31
  5. ADVICE - EB8 versus 12V adapter to monitor power
    By Detour in forum Misc Apex Usage & Programming
    Replies: 5
    Last Post: 01-01-2014, 17:16

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •