    ATK not working with APEX

    Good morning
    i bought the Apex this week installed it was having some issues with.
    but thought I had resolved them
    i doublechecked everything last night again ( Thursday night it didn't fill anything and I got alarms)
    and I didn't get any alarms or anything but this morning again it didn't fill
    i unplugged it set it back to stand alone mode ( via the reset button)
    and it filled right away
    I know that I will probably need to uninstall it all and redo it but want to check if this code is ok

    Fallback OFF
    Set OFF
    If ATO_LO OPEN Then ON
    If ATO_HI CLOSED Then OFF
    When On > 010:00 Then OFF
    Defer 000:10 Then ON
    Defer 000:04 Then OFF
    Min Time 060:00 Then OFF


    Thanks

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Looks fine. Just make sure your optical sensors are set at optical and not water on the floor.

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    Frequent Visitor bescher's Avatar
    Join Date
    Dec 2014
    Location
    Nashotah WI
    Posts
    204
    Quote Originally Posted by zombie View Post
    Looks fine. Just make sure your optical sensors are set at optical and not water on the floor.

    You might be an engineer if...You have no life and can prove it mathematically.
    I have removed it from the apex but won't add it on till after Tuesday probably it works in stand alone and yes I made sure they were in optical also that virtual outlet I created per your instructions where do I put that code into the ATO-LO button?

    thank much Zoombie

  4. #4
    Frequent Contributor iamchadster's Avatar
    Join Date
    Aug 2013
    Location
    Wilsonville, Oregon
    Posts
    2,642
    Couple thoughts. Do you have logging enabled for that outlet?See if it's ever coming on. In theory a quick open and close of that optical sensor, the min time off may be keeping it off longer than what you need.

    I removed the min time off statement from mine and actually made a min time on statement instead to minimize the on off cycles so much.
    Chad

  5. #5
    Frequent Visitor bescher's Avatar
    Join Date
    Dec 2014
    Location
    Nashotah WI
    Posts
    204
    Quote Originally Posted by iamchadster View Post
    Couple thoughts. Do you have logging enabled for that outlet?See if it's ever coming on. In theory a quick open and close of that optical sensor, the min time off may be keeping it off longer than what you need.

    I removed the min time off statement from mine and actually made a min time on statement instead to minimize the on off cycles so much.
    Good morning I don't have it hooked into the Aoex I removed everything will work on it the coming week but will log it

    thsnks

  6. #6
    Frequent Visitor bescher's Avatar
    Join Date
    Dec 2014
    Location
    Nashotah WI
    Posts
    204
    Quote Originally Posted by iamchadster View Post
    Couple thoughts. Do you have logging enabled for that outlet?See if it's ever coming on. In theory a quick open and close of that optical sensor, the min time off may be keeping it off longer than what you need.

    I removed the min time off statement from mine and actually made a min time on statement instead to minimize the on off cycles so much.
    Hi Zombie and I truly appreciate all your help but questions
    im trying to figure out the below suggestion. I'm not that good with virtual outlets
    but where will I put the below that you gave me to ensure that my ATK doesn't sound a alarm and stays off while I'm feeding

    i did create the virtual outlet

    sorry about the large font but I copied and pasted

    To stop the alarm in the event your return is off, You need a virtual outlet. Replace return with your return pump name, and adjust the defer length so it is about 1.5 to 2 times the amount of time it takes for water level to return to normal after the return pump turns back on.


    HighH2O
    Set OFF
    If ATO_HIGH CLOSED Then ON
    If Outlet ReturnPu3_2 = OFF Then OFF
    Defer 001:00 Then ON


    Email (remove your ato_high statement)
    (Existing code)
    If Outlet HighH2O = ON Then ON

  7. #7
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    HighH2O is the virtual outlet you created.

    The other line goes in your email alarm instead of the switch statement you have now.

    You might be an engineer if...You have no life and can prove it mathematically.

  8. #8
    Frequent Visitor bescher's Avatar
    Join Date
    Dec 2014
    Location
    Nashotah WI
    Posts
    204

    Atk not working with Apex

    Quote Originally Posted by zombie View Post
    HighH2O is the virtual outlet you created.

    The other line goes in your email alarm instead of the switch statement you have now.

    You might be an engineer if...You have no life and can prove it mathematically.
    So this code goes into my virtual outlet then?
    Set OFF
    If ATO_HIGH CLOSED Then ON
    If Outlet ReturnPu3_2 = OFF Then OFF
    Defer 001:00 Then ON

  9. #9
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Correct

    You might be an engineer if...You have no life and can prove it mathematically.

Similar Threads

  1. Help! Apex ATK not working
    By wonderphilreef in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 2
    Last Post: 05-09-2022, 02:31
  2. help my ATK is not working
    By rpattek in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 12
    Last Post: 10-21-2019, 11:34
  3. Question: ATK seems to be working, but...
    By Jcat2k in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 2
    Last Post: 01-20-2019, 12:19
  4. Help! ATK Not working
    By Deitz in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 4
    Last Post: 10-05-2018, 16:43
  5. Help! Atk not working
    By whytey963 in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 15
    Last Post: 10-10-2017, 16:59

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •