Hey guys, I helped a buddy set up a new Classic system today and am running into an issue with the ATO. I have use the following program and have no issues on my classic and 2016 units. The program runs fine on his until the reservoir float comes in. The switch in the reservoir isnt shutting off the top off pump when the reservoir is empty. The program is as it stands currently is;
ATO_Pump
Fallback OFF
Set OFF
If Outlet Sump_Low = ON Then ON
If Outlet Sump_High = ON Then OFF
If Outlet Res_Empty = ON Then OFF
Sump_Low
If Sw1 CLOSED Then ON
If Sw1 OPEN Then OFF
Sump_High
If Sw2 CLOSED Then ON
If Sw2 OPEN Then OFF
Res_Empty
If Sw3 Closed Then ON
If Sw3 OPEN Then OFF
I have a feeling Im missing something obvious. Any suggestions or improvements are welcome and appreciated!