Change your HighH2O code back to what it was in post number 5. Your email should be this.
Set OFF
If Tmp > 80.0 Then ON
If Tmp < 74.0 Then ON
If Floor CLOSED Then ON
If Cabine CLOSED Then ON
If SUMP6 CLOSED Then ON
If Error ATK_Alarm Then ON
If Outlet HighH2O = ON Then ON
If you get the If Error ATK_Alarm in an email, that means the pump ran longer than 5 minutes and set itself to off. Get the level correct in your tank to start and if that alarm ever goes off then either there is a problem you need to address (clogged line, empty reservoir, cracked line, etc.). If no problem is found, then that means 5 minutes isn't long enough on the when statement and that needs to be larger.
Don't forget to turn the ATK outlet back to auto if you get the If Error email.