Fallback OFF (turns off if comms are lost to base unit)
Set OFF (defaults to off)
If ATK_LO OPEN Then ON (turns on if water level is low)
If ATK_HI CLOSED Then OFF (turns off if water level is high)
If ResLow OPEN Then OFF (turns off is reservoir is empty)
When On > 005:00 Then OFF (sets pump to manual off if timer is exceeded)
Defer 000:10 Then ON (keeps pump from short cycling)
Defer 000:04 Then OFF (keeps pump from short cycling)
Min Time 060:00 Then OFF (keeps pump from short cycling)