    Optical float switches in DDR failed

    The optical level sensors in my DDR are both reporting closed though both sides are nearly full. It started with one and now both are wrong. They are clean and this unit is only a couple months old. Any advice would be appreciated.

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    Frequent Visitor
    Join Date
    Nov 2016
    Location
    Slidell La
    Posts
    93
    Im not the brightest crayon in the box with apex yet, though I do have the DDR and when full of fluid they are supposed to read closed.
    Only read Open when the fluid level is below the sensor.
    Am I missing something here or maybe you worded it wrong== open/ closed ?

  4. #4
    Regular Vistor
    Join Date
    Aug 2016
    Location
    Atlanta, GA
    Posts
    20
    I may be mistaken about where they should be but they are definitely closed now and they were open for weeks and the level has been way above them all along. lol

  5. #5
    Frequent Visitor
    Join Date
    Nov 2016
    Location
    Slidell La
    Posts
    93
    Quote Originally Posted by Arringar View Post
    I may be mistaken about where they should be but they are definitely closed now and they were open for weeks and the level has been way above them all along. lol
    If they are full of fluid or the fluid is above the optical sensors and the switches are reading closed then its working as it should.
    Remove the fluid in them or wait until its used up and gets below the sensor, if the switches open up then its working normal as it should.
    When you fill them back above the optical sensor the switch should go back to reading closed.

Similar Threads

  1. Replace ATK Optical Switches With Float Switch
    By bigjim in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 2
    Last Post: 07-30-2018, 05:21
  2. FMM Optical Switches vs BOB Float Switch
    By Tha Bizness in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 5
    Last Post: 08-02-2017, 06:03

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •