    Question Possible to get an alarm when the condenser is running?

    I'm curious to know if the Apex can send emails when the condenser is actually running. I'm thinking the output is using more than X kilowatt when the condenser is running then when it's just simply on?

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Yes, but it will get real annoying real fast. Much better option is to send an email when the condenser is running and the wattage draw is outside of normal limits.

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    Frequent Visitor
    Join Date
    May 2017
    Location
    Los Angeles, CA
    Posts
    110
    Quote Originally Posted by zombie View Post
    Yes, but it will get real annoying real fast. Much better option is to send an email when the condenser is running and the wattage draw is outside of normal limits.

    You might be an engineer if...You have no life and can prove it mathematically.
    That's exactly what I want. Must have not phrased it correctly. Do you have a sample code I can look at?


    Sent from my iPhone using Tapatalk

  4. #4
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,463

    Possible to get an alarm when the condenser is running?

    https://www.neptunesystems.com/getst...reak-advanced/.

    See the Advanced alarms topic. Pick the Watts input which corresponds to the chiller’s EB832 outlet. For example, if the outlet is named Chilller, the watts input will be ChillerW. Set the high and low alarm triggers as desired.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  5. #5
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Fringe09 View Post
    That's exactly what I want. Must have not phrased it correctly. Do you have a sample code I can look at?


    Sent from my iPhone using Tapatalk
    Create a virtual outlet. (I am assuming below your outlet is called Chiller). With a condenser, IME the guide is wrong to suggest using watts for the high value. What you want is amp draw because a stall in the condenser will only increase watts a small amount (20% or so) whereas amps will be 4-6 times normal level. Set X to be 75% of normal wattage draw. Set Y to be 150% or normal amp draw.

    ChillFail
    Set OFF
    If Output Chiller Watts < X Then ON
    If Output Chiller Amps > Y Then ON
    If Outlet Chiller = OFF Then OFF
    Defer 000:10 Then ON

    Email
    (Existing code)
    If Outlet ChillFail = ON Then ON

    You might be an engineer if...You have no life and can prove it mathematically.

  6. #6
    Frequent Visitor
    Join Date
    May 2017
    Location
    Los Angeles, CA
    Posts
    110
    Quote Originally Posted by zombie View Post
    Create a virtual outlet. (I am assuming below your outlet is called Chiller). With a condenser, IME the guide is wrong to suggest using watts for the high value. What you want is amp draw because a stall in the condenser will only increase watts a small amount (20% or so) whereas amps will be 4-6 times normal level. Set X to be 75% of normal wattage draw. Set Y to be 150% or normal amp draw.

    ChillFail
    Set OFF
    If Chiller Watts < X Then ON
    If Chiller Amps > Y Then ON
    If Outlet Chiller = OFF Then OFF
    Defer 000:10 Then ON

    Email
    (Existing code)
    If Outlet ChillFail = ON Then ON

    You might be an engineer if...You have no life and can prove it mathematically.
    Thank you for this! I'll try it when I get home.


    Sent from my iPhone using Tapatalk

  7. #7
    Frequent Visitor
    Join Date
    May 2017
    Location
    Los Angeles, CA
    Posts
    110
    Quote Originally Posted by RussM View Post
    https://www.neptunesystems.com/getst...reak-advanced/.

    See the Advanced alarms topic. Pick the Watts input which corresponds the chiller’s EB832 Outlet. For example, if the outlet is named Chilller, the watts input will be ChillerW. Set the high and low alarm triggers.
    Thank you.


    Sent from my iPhone using Tapatalk

  8. #8
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Fringe09 View Post
    Thank you for this! I'll try it when I get home.


    Sent from my iPhone using Tapatalk
    See my updates. I accidentally made a syntax error and corrected above.

    You might be an engineer if...You have no life and can prove it mathematically.

Similar Threads

  1. Help! Recurrent alarm for digital switch that isnt in alarm state
    By jeremym in forum APEX Fusion
    Replies: 5
    Last Post: 12-20-2019, 16:08
  2. Replies: 3
    Last Post: 03-11-2019, 08:08
  3. Pulling an alarm for the wrong outlet, that doesn't need an alarm.
    By Scott.h in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 3
    Last Post: 12-03-2016, 09:24
  4. Error programming e-mail alarm ( any alarm )
    By cypherljk in forum WAV Powerheads
    Replies: 4
    Last Post: 09-27-2016, 12:22
  5. Replies: 4
    Last Post: 08-25-2014, 11:41

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •