Added a new flowmeter onto a 1/2" hose to a reactor but try as I might the FMM won't recognize the new 1/2" flowmeter probe plugged into Port 2. FMM reports it as "Unknown Sensor". Any tips or hints?
Sent from my iPad using Tapatalk
Added a new flowmeter onto a 1/2" hose to a reactor but try as I might the FMM won't recognize the new 1/2" flowmeter probe plugged into Port 2. FMM reports it as "Unknown Sensor". Any tips or hints?
Sent from my iPad using Tapatalk
What happens if you uncheck "use auto detection" and select the sensor type in the drop down menu?
Chad
I tried that last night with out a result. Tried again this morning and bingo! Fluidized Reactor Flow "FLRFLO" is reading fine.
Sent from my iPad using Tapatalk