Thread: How to avoid triggering an alarm after Feed Mode

  1. #1
    New User
    Join Date
    Sep 2017
    Location
    US, Central Time
    Posts
    6

    How to avoid triggering an alarm after Feed Mode

    Hey Guys,

    I've racked my brain trying to do defer commands and simple on off commands, but I can't figure out how to make this work.

    -I have an alarm that changes the colors of my Radions when it trips.
    -I have a trigger for the alarm that will trip it when ATK_Hi switch is CLOSED
    -I activate FeedD (or any of them) and in my Alarm programming I specify "If FeedD 000 Then OFF" which keeps the alarm from triggering WHEN I ACTIVATE FeedD.
    -My problem is that once Feed D ends, the alarm sees that FeedD is over and the ATK_Hi switch is still closed since the Vectra hasn't moved all of the water back into the main tank, and it trips the alarm.

    How do I avoid the alarm being tripped AFTER FeedD turns off?

    Joshua

  2. #2
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    If FeedD 005 Then OFF in your alarm programming. Alarm won't be enabled for 5 minutes after your FeedD ends. Although I believe that if you cancel it manually, the delay is ignored, which would mean you'd get the alarm in that case. (I haven't checked that last part personally so someone please correct me if I'm wrong. )

  3. #3
    New User
    Join Date
    Sep 2017
    Location
    US, Central Time
    Posts
    6
    It hurts my brain when these things are so simple... Lol

    Any way to 'hard' prevent it? Even if FeedD is cancelled?

  4. #4
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    Yes. You could put a blanket 1 or 2 minute Defer command in your email/text/alarm programming. It would render your notification slightly less instantaneous, but will avoid false alarms due to temporary disequilibrium situations like the end of a feed cycle. Or, alternatively, you can put a Defer in your ATK Hi switch closed programming. As long as it's small, like a minute or two, the risk is low and the benefit considerable. You could even do both as long as you're careful.

    I put small Defers in much of my Apex programming. It smooths out the whole experience.

  5. #5
    New User
    Join Date
    Sep 2017
    Location
    US, Central Time
    Posts
    6
    You're the best- Thanks!!

  6. #6
    New User
    Join Date
    Oct 2017
    Location
    BROOKLYN
    Posts
    9
    I believe a similar solution would work for me but I'm unsure what the coding would be and where to enter it. Because of space constraints in my sump, my ATO with Kalkwasser gets put into the system close to my probes thus giving a false spike for one reading.
    Could you please assist?
    Thanks!!

Similar Threads

  1. How to stop alarm when in feed mode
    By tiatank in forum APEX Fusion
    Replies: 0
    Last Post: 03-23-2022, 04:25
  2. alarm keeps triggering
    By reachjohnnyliu in forum APEX Fusion
    Replies: 3
    Last Post: 11-19-2021, 06:56
  3. Flow meter alarm goes off every time in feed mode
    By tiatank in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 7
    Last Post: 03-09-2020, 11:00
  4. FM Alarm Delay for Feed Mode?
    By chadowens in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 3
    Last Post: 01-30-2018, 06:49
  5. triggering dos with feed mode
    By jelly in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 7
    Last Post: 07-04-2016, 08:44

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •