Thread: Help with my Chiller and Heater program

  1. #1
    New User
    Join Date
    Dec 2015
    Location
    Canada
    Posts
    8

    Help with my Chiller and Heater program

    I just added a chiller to my system almost a week ago and was using this programming to keep my temps between 76-78F, which worked well:

    [Chiller]
    Fallback OFF
    If Temp > 78.0 Then ON
    If Temp < 77.0 Then OFF
    If Output ReturnPump = OFF Then OFF
    Defer 001:00 Then ON

    [Heater]
    Fallback OFF
    If Temp < 76.0 Then ON
    If Temp > 77.0 Then OFF
    If Temp < 70.0 Then OFF
    Defer 001:00 Then ON

    [ChillerPump]
    Fallback ON
    OSC 000:00/001:00/239:00 Then ON
    If Output Chiller = ON Then ON
    Defer 001:00 Then OFF

    With the program above I noticed my chiller running on and off every hour (one hour on, one hour off, etc). Today I found out my chiller manufacturer recommends a minimum of 2-3 degree variance to reduce cycling on and off. I've updated the program as follows and wondering if this suffice or will it conflict with my heater program:

    [Chiller]
    Fallback OFF
    If Temp > 78.0 Then ON
    If Temp < 76.0 Then OFF
    If Output ReturnPump = OFF Then OFF
    Defer 001:00 Then ON

    [Heater]
    Fallback OFF
    If Temp < 76.0 Then ON
    If Temp > 77.0 Then OFF
    If Temp < 70.0 Then OFF
    Defer 001:00 Then ON

    [ChillerPump]
    Fallback ON
    OSC 000:00/001:00/239:00 Then ON
    If Output Chiller = ON Then ON
    Defer 001:00 Then OFF

    Any help will be greatly appreciated.

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    That will most likely conflict with your heater as there is some latent cooling that will occur even after it turns off. I would personally increase the low threshold up at least a half a degree.

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    Quote Originally Posted by neeper View Post
    If Temp < 70.0 Then OFF
    Is this line to guard against a failed temp probe reading low and causing the heater to run away and cook everything?

    Would this generally be used with heaters that don't have an internal thermostat?

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by rkpetersen View Post
    Is this line to guard against a failed temp probe reading low and causing the heater to run away and cook everything?

    Would this generally be used with heaters that don't have an internal thermostat?
    Yes. If using only one heater with a internal thermostat it should not be used. If using 2 or more heaters its best to use that on just one so that the temp doesnt quickly spike if it wigs out. If using one without a thermostat that line is essential.

    You might be an engineer if...You have no life and can prove it mathematically.

Similar Threads

  1. Chiller / Heater code
    By jamiequ in forum Apex Programming for Heaters and Chillers
    Replies: 2
    Last Post: 10-10-2019, 06:47
  2. heater and chiller cycling on after the other...
    By kengeroo in forum Apex Programming for Heaters and Chillers
    Replies: 0
    Last Post: 10-27-2016, 06:25
  3. Review My Program chiller/ heater
    By Bswaff12 in forum Apex Programming for Heaters and Chillers
    Replies: 2
    Last Post: 08-06-2016, 14:42
  4. Question: Chiller and heater program check please
    By Bswaff12 in forum Apex Programming for Heaters and Chillers
    Replies: 2
    Last Post: 07-21-2016, 15:37
  5. Sample Program - Basic heater and chiller code
    By aquamanic in forum Apex Programming for Heaters and Chillers
    Replies: 0
    Last Post: 01-05-2013, 11:37

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •