    ATK Alarms with ZEOvit Reactor

    I use the ATK as my auto top off, and I would like some opinions on an “issue” I’m having. I use a ZEOvit reactor that I have turn on and off in 3 hour intervals. When it turns off, the water level in the sump raises up enough to trigger the back up water level sensor, so the alarm goes off. I’d like to program the alarm so that:

    If <backup sensor> = on AND If <ZEOvit reactor> = off AND If <atk pump> = off, alarm = off

    Does this logic make sense to you? Does it seem like it is too risky? How would I actually script that logic in Fusion?

  2. #2
    Apex User zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    6,619
    You need a virtual outlet and I would suggest this programming approach. Adjust the defer length so that it is long enough to allow water level to settle after the return turns back on or the ZeoVit turns off.

    HighH2O
    Set OFF
    If HighSw CLOSED Then ON
    If Outlet ReturnPump = OFF Then OFF
    If Outlet ZeoVit = ON Then OFF
    Defer 005:00 Then ON

    Email
    (Existing code)
    If Outlet HighH2O = ON Then ON


    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    New User
    Join Date
    Jun 2017
    Location
    Fort Worth, TX
    Posts
    2
    Works like a charm... thank you, friend!