I have a pump on an outlet on an EB8 that runs the flow through my chiller. I obviously only want it on when the chiller is running (using the Apex temp probe to turn it on and off). However, so I don’t get stagnant water in the chiller, I also want it to run for 5 minutes each morning, just to give it a good flush.
I start with the basics:
Fallback OFF
Set OFF
Then add my temp program:
If temp > 79 then ON
If temp < 78 then OFF
But I also add the line:
If time 5:00 to 5:05 then ON
A few weeks ago, it wasn’t turning off, so I added the “Set” line. Then, it didn’t go on and just chilled itself with no flow the next day. I think I’m lacking some understanding in the “Fallback” and “Set” commands.
Help?