    Zeomatic Control code

    Hey Guys,

    I'm a newbie with the APEX but it's definitly awesome by now... I'm just trying to control my zeolite reactor with it but I have difficulties with the code.

    I would like to Set ON the pump every 2 hours during 2min, can someone help me about the code? :-)

    Thanks !

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,492

    Zeomatic Control code

    Fallback OFF
    OSC 0/2:00/118:00 Then ON

    Will turn the outlet on for 2 minutes out of every 2 hours
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    New User
    Join Date
    Jun 2017
    Location
    Paris
    Posts
    13
    Quote Originally Posted by RussM View Post
    Fallback OFF
    OSC 0/2:00/118:00 Then ON

    Will turn the outlet on for 2 minutes out of every 2 hours
    Thanks, how can I set the start time?

  4. #4
    Frequent Visitor
    Join Date
    Jan 2016
    Location
    Cincinnati, ohio
    Posts
    709
    Look up the OSC command in the comprehensive reference manual to fully understand it as well as all the commands. That way you can figure this stuff out in the future.

    regarding the start time. If the total time in the command is divided evenly into 24 hours then the start time is midnight

Similar Threads

  1. Review My Program Need Help Converting Pseudo Code To APEX Code
    By bpeders1 in forum Misc Apex Usage & Programming
    Replies: 2
    Last Post: 07-24-2022, 16:13
  2. Apex Code Question: Day of Week Control
    By robram27 in forum Misc Apex Usage & Programming
    Replies: 7
    Last Post: 10-09-2020, 06:06
  3. Revising my AFS code - looking for some verification of code
    By rbarr110 in forum Misc Apex Usage & Programming
    Replies: 4
    Last Post: 10-21-2019, 12:17
  4. Could this code work to utilize my DOS as an ATO pump, and How would I add the code?
    By alexx2208 in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 4
    Last Post: 08-17-2017, 08:56
  5. Replies: 2
    Last Post: 09-11-2013, 05:36

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •