    I have a tetra heater that is auto set to 78. I'd like to set up apex as a redundancy if it every stays in the on position for Apex to shut it off after 82. This is how I have it setup in apex but when I set it to auto the heater says it's off and the temp will get down below 76 without it turning on. What am I doing wrong?
    Apex Heater.PNG

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,463
    The Heater Control Type is for use when the Apex is the primary control for the heater.

    Most people prefer to use the Apex as primary control and use the heaters built-in thermostat as the backup. But if you want to go with your current approach, you will need to use Advanced Control Type, then use this program:

    Fallback ON
    Set ON
    If Temp > 82.0 Then OFF
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    Frequent Visitor
    Join Date
    Jan 2016
    Location
    Cincinnati, ohio
    Posts
    709
    Your issue is that the outlet had nothing to turn it on until the temp dropped below 73.

    and I 100% agree with Russ on his comments above.

  4. #4
    Frequent Visitor Todd's Avatar
    Join Date
    Jan 2013
    Location
    Huntsville, AL
    Posts
    583
    +1 for Russ' recommendation. The Apex has a much better accuracy and can control over a tighter range. I like to control at a given temp +/- a tolerance. So if you want to keep the tank at 78 +/- .5, set the On Temp to 77.6 and the Off Temp to 78.4. That would give you a range of 77.5 to 78.5. Then set your heater thermostat to 82 if that is your desired safety point. If you have cooling fans, make sure there is no overlap in the temp range or they will be fighting each other and wasting energy.

  5. #5
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    I would concur as well. Not only do you get tighter temp control, you also increase the lifespan of the heater because you don't wear out the contacts that turn on/off based on temp.

    You might be an engineer if...You have no life and can prove it mathematically.

  6. #6
    New User
    Join Date
    Oct 2017
    Location
    Columbus, OH
    Posts
    5
    Thank you so much everybody for your input. I originally purchased the apex jr with the intent of using it control my heater, however doesn't it wear out the relay switch? My heater doesn't have an adjustable thermostat, it's auto set to 78, which it keeps within 1 degree, which I feel is pretty good. The heater was cheap and easily replaceable, the apex jr not as much. Thoughts?

  7. #7
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    The relays do eventually wear out but can handle about 100-1000 times more switches than your typical heater before wearing out (usually good for 8-10 years of tight temp control with 0.3 degree hysteresis). If your heater is auto set, I would just use the code Russ gave you for the time being. Down the road when the heater is ready for replacement, I would get one with a digital thermostat and let the apex take primary control.

    You might be an engineer if...You have no life and can prove it mathematically.

  8. #8
    New User
    Join Date
    Oct 2017
    Location
    Columbus, OH
    Posts
    5
    Quote Originally Posted by RussM View Post
    The Heater Control Type is for use when the Apex is the primary control for the heater.

    Most people prefer to use the Apex as primary control and use the heaters built-in thermostat as the backup. But if you want to go with your current approach, you will need to use Advanced Control Type, then use this program:

    Fallback ON
    Set ON
    If Temp > 82.0 Then OFF
    When fallback is set to on does that mean that the default position of the switch is on and so if something were to happen to the heater where it would stay in the on posiition would it stay on past my off temp or would it kick off?

  9. #9
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Fallback ON means in the event that the energy bar loses communications with the base unit, keep the outlet ON until communications is restored.

    You might be an engineer if...You have no life and can prove it mathematically.

  10. #10
    Frequent Visitor
    Join Date
    Jan 2016
    Location
    Cincinnati, ohio
    Posts
    709
    I suggest you download and read the comprehensive reference manual located in the Neptune links at the top of the page. It describes all the programming code.

Similar Threads

  1. Auto backup of Apex
    By Gbrugger in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 2
    Last Post: 10-26-2022, 21:28
  2. Controlling backup heater with power of the main heater.
    By rlozano in forum Apex Programming for Heaters and Chillers
    Replies: 1
    Last Post: 01-19-2021, 16:27
  3. Apex and Nest Thermostat
    By techdef in forum DIY
    Replies: 6
    Last Post: 09-07-2016, 08:25
  4. Help! Apex thermostat for radiant heating loop
    By lakereef in forum Apex Programming for Heaters and Chillers
    Replies: 29
    Last Post: 02-14-2016, 19:38
  5. Check My Program: Heater w/ Thermostat (Safeguards?)
    By Spoon in forum Apex Programming for Heaters and Chillers
    Replies: 25
    Last Post: 05-25-2014, 10:22

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •