    Apex FMM ATO

    Hello

    im not new to apex but new to this site and not very good when technical things do not work like they say they should out of the box.

    recently purchased the above kit after my D and D failed and but 150ltrs of fresh water into my tank.

    updated firmware on the FMM but can not seem to get this working even though it’s above the water line.only way I can get it to work is to turn the pump to ON on the apex fusion app.

    i have attached a photo of what code apex Has automatically installed
    Attached Images Attached Images

  2. #2
    New User
    Join Date
    Nov 2017
    Location
    Uk
    Posts
    8
    Also just received this alarm

    2017-11-24 18:27:37 +0000 ON If Error ATO Then ON

  3. #3
    Frequent Visitor Todd's Avatar
    Join Date
    Jan 2013
    Location
    Huntsville, AL
    Posts
    583
    I am assuming that Sw9_1 is a nominal level and Sw9_2 is a safety maximum level. If so, then the ATO will come ON 10 secs after the water has dropped below Sw9_1. Then it will run until 4 secs after reaching the sensor again. Once it shuts OFF, the Min Time command will keep it OFF for 60 minutes regardless of water level. In addition, while filling, if total run time exceeds 5 minutes, then it will shutoff into manual mode and throw the error.

  4. #4
    New User
    Join Date
    Nov 2017
    Location
    Uk
    Posts
    8
    Thanks todd

    just going to leave it 24hrs and see what happens to my water level as i have messed about with it quit a bit

  5. #5
    New User
    Join Date
    Nov 2017
    Location
    Uk
    Posts
    8
    I have just reset the FMM module after taking out the aqua bus cable linking it to apex so now it’s working on stand alone mode.

    its seems to be working so when I plug it into apex it does not work ?.

    why is this so hard to do

  6. #6
    Frequent Visitor Todd's Avatar
    Join Date
    Jan 2013
    Location
    Huntsville, AL
    Posts
    583
    Have you checked for duplicate modules or names? Can you see the status of each switch and is it what you expect it to be?

  7. #7
    New User
    Join Date
    Nov 2017
    Location
    Uk
    Posts
    8
    After connecting the FMM module I had 5 new tiles

    SWX9_1
    SWX9_2
    SWX9_3
    SWX9_4
    then the ATO

    wich is now now off because it’s now set up as stand alone
    Attached Images Attached Images

  8. #8
    New User
    Join Date
    Nov 2017
    Location
    Uk
    Posts
    8
    So I now have The FMM module connected back to apex.

    the SWX9_1 was in the closed position and the SWX9_2 is in the open position which I believe is correct.

    i have now raised SWX9_1 out of the water and the switch went from closed to open meaning apex should tell the pump to turn on but nothing happens

    - - - Updated - - -

    Back to stand alone mode until the morning I believe
    Attached Images Attached Images

  9. #9
    Frequent Visitor Todd's Avatar
    Join Date
    Jan 2013
    Location
    Huntsville, AL
    Posts
    583
    It seems the sensors are working correctly, but it will be hard to troubleshoot with the Defer(s), and Min Time statements. They add delays and lockouts. I suspect it is the Min Time that is giving you the problem since it holds the state OFF for an hour. If you are comfortable with the advanced programming mode, then set the Defer(s) and Min Time to 1 second and experiment.

  10. #10
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    Confirming that you have the pmup plugged into the ACC port on the FMM, and the separate power supply also plugged into the FMM PWR port, even when running under Apex.

    Also agree with suggestion to experiment with the code a bit. Here's mine, works great, feel free to try it with your system (with appropriate name modifications.)

    Fallback OFF
    Set OFF
    If ATOLo OPEN Then ON
    Defer 002:00 Then ON
    Min Time 030:00 Then OFF
    When On > 002:00 Then OFF
    If Sal < 33.0 Then OFF
    If ATOHi CLOSED Then OFF
    If LeakRO CLOSED Then OFF
    If RODILo OPEN Then OFF
    If FeedA 000 Then OFF
    If FeedB 000 Then OFF
    If FeedC 000 Then OFF
    If FeedD 000 Then OFF
    If Output ReturnPump = OFF Then OFF
    If Output LeakDetected = ON Then OFF
    Defer 000:05 Then OFF

  11. #11
    Regular Vistor
    Join Date
    Sep 2013
    Location
    Treasure Coast Florida
    Posts
    34
    Would it be better to take the safety's off get it working then one by one add them till it fails?

  12. #12
    New User
    Join Date
    Nov 2017
    Location
    Uk
    Posts
    8
    Thanks for all the reply’s I will try them and see if they work

Similar Threads

  1. 2 FMM for 1 ATO
    By Grayhead in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 5
    Last Post: 01-21-2022, 09:36
  2. Using apex unit instead of FMM for ATO and progragrming
    By RZR72 in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 1
    Last Post: 12-12-2021, 09:04
  3. Can I use my new ATO/FMM module to also run my Leak Detection sensor from my Apex Classic?
    By deputydog95 in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 4
    Last Post: 07-31-2020, 08:30
  4. FMM (ATO) vs FMM (LDK)
    By marineboy in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 1
    Last Post: 07-18-2019, 07:27
  5. Question: FMM/ATO issues when ATO reservoir is refilled
    By Faulker's Maze in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 12
    Last Post: 12-14-2018, 11:43

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •