    upgraded base station to new 2016 model. old programing not working

    I have the following program running for an outlet on a eb8, the input (rodi) comes from a pressure switch connected to a pm2. all this was working on the old classic base station. but this outlet remains off no matter what the pressure switch inputs.

    outlet Water:
    "fallback OFF
    If RODI CLOSED Then ON
    If RODI OPEN Then OFF"

    i have confirmed the switches are working. I do have another outlet, same eb8, same pm2 inputs, also not responding, but a third working just fine?
    also not working outlet saltfill: "Fallback OFF
    If Sltmt OPEN Then on
    If SltFul CLOSED Then OFF"

    but working just fine outlet mixingpumps: "Fallback OFF
    Set ON
    If Sltmt OPEN Then OFF"

  2. #2
    NSI Member Krazie4Acans's Avatar
    Join Date
    Nov 2013
    Location
    US, Mountain Time
    Posts
    1,257
    You aren't setting a default state for the outlets that aren't working in your programming. Add Set OFF after the Fallback lines on each outlet and see if that doesn't fix it.

    FYI, setting outputs to come ON when a switch is open is generally a bad idea because switches normally fail in the open position.

  3. #3
    Regular Vistor
    Join Date
    Oct 2015
    Location
    central
    Posts
    37
    I’ve tried adding a set statement which didn’t do anything, it would also defeat the whole programming of my saltfill outlet. i'd like to still point out all this programing above worked perfectly on my apex classic

    As for the fail open statements, there are redundant back ups to kick in should one fail.


    Sent from my iPhone using Tapatalk

  4. #4
    Frequent Visitor
    Join Date
    Jan 2016
    Location
    Cincinnati, ohio
    Posts
    709
    Just to clarify, you confirmed the switches are working, but have you confirmed that the Apex us recognizing the switch operation? I.e is fusion showing the switches closed?

    also, simple and obvious, is the outlet set to auto?

  5. #5
    Regular Vistor
    Join Date
    Oct 2015
    Location
    central
    Posts
    37
    Quote Originally Posted by Frogfish View Post
    Just to clarify, you confirmed the switches are working, but have you confirmed that the Apex us recognizing the switch operation? I.e is fusion showing the switches closed?

    also, simple and obvious, is the outlet set to auto?
    Yes, I did confirm that the switches are seen and working in fusion. And the outlets are set to auto.


    Sent from my iPhone using Tapatalk

  6. #6
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,489
    Make sure that you have not inadvertently given two different switch inputs the same names.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

Similar Threads

  1. Help! Swapping base 2016 base unit
    By Alfisreef in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 9
    Last Post: 03-26-2022, 13:44
  2. Painless classic to 2016 model
    By jamiequ in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 5
    Last Post: 03-15-2018, 05:56
  3. UK Spec 2016 Model
    By tastyfish in forum Pre-Sales Questions
    Replies: 42
    Last Post: 03-03-2018, 03:30
  4. Painless classic to 2016 model
    By jamiequ in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 1
    Last Post: 11-15-2017, 03:20
  5. Is there Documentation for the Apex 2016 Model?
    By Salty Hands in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 1
    Last Post: 01-24-2017, 21:34

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •