    Dual Finnex heaters

    I have 2 300 watts finnex heaters for my 100 gallon tank. I wanted to use Apex to control heaters and have the thermostat as a backup. My question is what should I put my finnex controller temp too? Also if my temp is between 78.1 and 78.4 I don't want the heater to be turning on and off every 5 seconds. I am looking to keep a mixed tank mostly sps and lps.


    Heater1
    Fallback ON
    If Temp < 78.1 Then ON
    If Temp > 78.4 Then OFF
    If Time 20:00 to 07:59 Then OFF
    If Temp < 77.9 Then ON

    Heater2
    Fallback OFF
    If Temp < 78.1 Then ON
    If Temp > 78.4 Then OFF
    If Time 08:00 to 19:59 Then OFF
    If Temp < 77.9 Then ON
    If Temp < 75.0 Then OFF

  2. #2
    Frequent Visitor
    Join Date
    Jan 2016
    Location
    Cincinnati, ohio
    Posts
    709
    You would set the internal thermostat to something like 79, so if the apex fails it doesn't go crazy in your tank.

    if your system is big enough to need a 300 watt heater, I doubt the temp will raise or fall 0.6 degrees in 5 seconds, probably could fall in 30 minutes and raise in an hour or so

  3. #3
    Regular Vistor
    Join Date
    Oct 2016
    Location
    New york
    Posts
    47
    I have a 100 gallon tank.

    - - - Updated - - -

    thanks for the feedback

  4. #4
    Average Member don_chuwish's Avatar
    Join Date
    Jan 2013
    Location
    Southern Oregon
    Posts
    65
    This one seems similar to my post last night. If using an external controller with it's own temp probe isn't it best to have the Apex outlet stay on unless/until some max temp threshold is reached? In other words, let the Finnex controller do all the normal temp monitoring & adjusting and just have Apex turn it off if Apex senses a temp too high?
    don_chuwish
    Southern Oregon

  5. #5
    Regular Vistor
    Join Date
    Oct 2016
    Location
    New york
    Posts
    47
    Don not sure I would think using apex is more precise than the controller. I would probably expect the therm controller to fail before apex.

  6. #6
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Nycluis View Post
    Don not sure I would think using apex is more precise than the controller. I would probably expect the therm controller to fail before apex.
    It's more precise and less likely to fail. The precise part is due to a more customizable hysteresis. By default most heaters have a 1.0 to 2.2 degree hysteresis range. The apex can get that down al low as 0.3. The less likely to fail is better contacts.

    You might be an engineer if...You have no life and can prove it mathematically.

Similar Threads

  1. Multiple returns and dual heaters
    By Morangus in forum Apex Programming for Heaters and Chillers
    Replies: 2
    Last Post: 02-04-2021, 19:42
  2. 2 Finnex Heaters Question
    By Mical in forum Apex Programming for Heaters and Chillers
    Replies: 3
    Last Post: 03-13-2020, 19:38
  3. Help! Dual 500 Watt Heaters Reefer 750 XXL
    By Diesel48 in forum Apex Programming for Heaters and Chillers
    Replies: 8
    Last Post: 03-23-2019, 18:04
  4. Finnex hmo 300 heaters
    By Nycluis in forum Apex Programming for Heaters and Chillers
    Replies: 3
    Last Post: 02-11-2018, 14:53
  5. Dual heaters
    By RickyRicardo in forum Apex Programming for Heaters and Chillers
    Replies: 3
    Last Post: 01-03-2014, 01:34

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •