    Fuge Light on EB8 Bar

    I have a question.. Is it ok to plug my fuge light into port 3 of the EB8 bar?

    Fallback OFF
    Set OFF
    If Time 22:00 to 08:00 Then ON
    If Tmp > 79.5 Then OFF
    If FeedA 000 Then OFF
    If FeedD 000 Then OFF

    From what I understand there are certain ports on the EB8 that are for certain things. Not sure what they are.

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    Chances are that your light will operate properly. But my supernatural powers are a bit weak this morning - especially those powers for long-distance mind reading. Tell us what you are using as a ‘fuge light so that someone might be able to answer your question.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    Regular Vistor
    Join Date
    Oct 2016
    Location
    New york
    Posts
    47
    Quote Originally Posted by RussM View Post
    Chances are that your light will operate properly. But my supernatural powers are a bit weak this morning - especially those powers for long-distance mind reading. Tell us what you are using as a ‘fuge light so that someone might be able to answer your question.
    I am running a refugium, so will be lighting and growing chaeto at night when my lights go off on the main display tank.

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    That will be fine. The issue of needing certain things on certain ports only applies to the EB8 and not the EB832. The rules for the EB8 are that low wattage inductive loads (like small pumps, aqualifters, dosing pumps, etc) must be put on outlets 4 or 8. This is to prevent a physical property with triacs from getting stuck ON when you turn them OFF. The other rule is that devices with a current draw between 5A and 10A must also be on 4 or 8 so you don't fry the outlet from overload.

    You might be an engineer if...You have no life and can prove it mathematically.

Similar Threads

  1. Question: Fuge light schedule was working, now is not
    By FishWish in forum Apex Programming for Lighting
    Replies: 2
    Last Post: 02-17-2019, 11:22
  2. Question: Fuge light
    By Theshaman in forum Apex Programming for Lighting
    Replies: 2
    Last Post: 01-20-2018, 22:17
  3. Fuge light of and on.
    By trimixdiver in forum Misc Apex Usage & Programming
    Replies: 8
    Last Post: 05-09-2016, 18:09
  4. Review My Program Fuge light help.
    By randoreefer in forum Apex Programming for Lighting
    Replies: 3
    Last Post: 12-02-2014, 13:31
  5. My fuge light will not turn on.
    By apw63 in forum Apex Programming for Lighting
    Replies: 6
    Last Post: 03-16-2013, 09:07

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •