    Apex Programming Capability

    Hey All, I Just ordered the Apex Classic yesterday but was wondering, Can the apex be programmed to use a single float switch as an input for two different circuits based on the input of a 3 way toggle switch. for instance, the float switch would primarily be used for Fresh water auto top off. if the toggle switch is in the up position, it controls the freshwater Top Off pump, but can i make that same switch tell the apex that if its in the down position, use that same float switch but control the Saltwater Top off pump. im looking to flip the switch in one position for freshwater top off to top off for evaporation, the flip it in the opposite position to control saltwater top off for when i remove water for water changes so it adds the exact same amount of water i took out and that way i wont have to deal with salinity fluctuations based on adding too much or too little saltwater, then flip the switch back to the freshwater position once the water change is done.

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Yep. Just use these two lines in their respective codes. I assume up is closed, which is the safest orientation.

    Freshwater
    (ATO code)
    If Switch OPEN Then OFF

    Saltwater
    (Refill code)
    If Switch CLOSED Then OFF

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    New User
    Join Date
    Dec 2017
    Location
    Florida
    Posts
    7
    So then this code would be put into the code section on the Saltwater Pump I am controlling? And for the Freshwater ATO code is that for when the toggle switch is in the middle, where Up is On, Middle is Off/Auto, and down is On? Or is this for a two way switch where Up is On(Closed circuit) and down is Off (Open circuit) with no middle. Sorry I’m just having trouble trying to wrap my head around it. Also how is the float switch wired? In series with the toggle switch? Or wired separately so the toggle switch would be input one on the BoB and the float switch would be input two?

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    That is for a two way toggle wires into a switch inout. For a three way toggle you would use two seperate switch inputs and use CLOSED for both where the middle disables both, up enables fresh and down enables salt. Wiring a toggle switch in series with a float would not help you here.

    You might be an engineer if...You have no life and can prove it mathematically.

  5. #5
    New User
    Join Date
    Dec 2017
    Location
    Florida
    Posts
    7
    So then how does the float switch get wired into this all (using the 3 way switch instead of the 2 way) to open up the Closed Circuits to tell the apex to turn either the freshwater or Saltwater Pump On? Also what would the code be for that as well. Sorry for all the questions

  6. #6
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    You would wire the float into a different input and use something like this as a starting point. I am calling the float ATOsw and HighSw (You should really have 2 for failsafe). I am calling the toggle ATOtog.

    ATO
    Fallback OFF
    Set OFF
    If ATOsw CLOSED Then ON
    If HighSw OPEN Then OFF
    If ATOtog OPEN Then OFF
    Defer 000:10 Then ON
    Defer 000:10 Then OFF
    When On > 005:00 Then OFF
    Min Time 060:00 Then OFF

    Saltwater
    Fallback OFF
    Set OFF
    If ATOsw CLOSED Then ON
    If HighSw OPEN Then OFF
    If ATOtog CLOSED Then OFF
    Defer 000:10 Then ON
    Defer 000:10 Then OFF

    You might be an engineer if...You have no life and can prove it mathematically.

  7. #7
    New User
    Join Date
    Dec 2017
    Location
    Florida
    Posts
    7
    Ok so then “Set Off” part of the code is what gets controlled via “ATOtog open” in the freshwater circuit correct? And if the apex loses power and can’t see anything then it tells the circuit to stay off via “Fallback Off”?

  8. #8
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Nope. Below is with comments

    ATO
    Fallback OFF//default to off if loses communications
    Set OFF//default OFF state
    If ATOsw CLOSED Then ON//turns pump on when normal level is reached
    If HighSw OPEN Then OFF//turns pump off if high switch is reached
    If ATOtog OPEN Then OFF//turns pump off if toggle in down position
    Defer 000:10 Then ON//debouncing
    Defer 000:10 Then OFF//debouncing
    When On > 005:00 Then OFF//sets pump to manual OFF if pump runs longer than 5 minutes
    Min Time 060:00 Then OFF//must be OFF for 1 hour since last fill before allowing another fill

    Saltwater
    Fallback OFF//default to off if loses communications
    Set OFF//default OFF state
    If ATOsw CLOSED Then ON//turns pump on when normal level is reached
    If HighSw OPEN Then OFF//turns pump off if high switch is reached
    If ATOtog CLOSED Then OFF//turns pump off if toggle in up position
    Defer 000:10 Then ON//debouncing
    Defer 000:10 Then OFF//debouncing


    You might be an engineer if...You have no life and can prove it mathematically.

  9. #9
    New User
    Join Date
    Dec 2017
    Location
    Florida
    Posts
    7
    Ohh ok I understand now, so ATOtog in the Up position enables the Freshwater circuit and ATOtog in the Down position enables the Saltwater circuit? And this is a 2 way switch right? With On/Off, not a 3 way switch which has On/Off/On, just to be clear? I also want to say thank you so much for all your help for breaking it down for me

  10. #10
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Mikedawg8898 View Post
    Ohh ok I understand now, so ATOtog in the Up position enables the Freshwater circuit and ATOtog in the Down position enables the Saltwater circuit? And this is a 2 way switch right? With On/Off, not a 3 way switch which has On/Off/On, just to be clear? I also want to say thank you so much for all your help for breaking it down for me
    Yep.

    You might be an engineer if...You have no life and can prove it mathematically.

  11. #11
    New User
    Join Date
    Dec 2017
    Location
    Florida
    Posts
    7
    Thank you so much, I truly appreciate all your help

Similar Threads

  1. Question: Programming New Apex before removing existing apex gold.
    By Cpage101 in forum Misc Apex Usage & Programming
    Replies: 2
    Last Post: 09-25-2019, 17:02
  2. Question: Programming my Apex
    By strat1960s in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 3
    Last Post: 02-11-2017, 06:23
  3. New to programming and Apex
    By Koddie Doo in forum Misc Apex Usage & Programming
    Replies: 0
    Last Post: 02-05-2014, 06:01
  4. Apex Jr. Capability
    By MikeEnright in forum Pre-Sales Questions
    Replies: 7
    Last Post: 05-21-2013, 03:28
  5. Help! Apex Programming Help
    By saltysailor2329 in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 7
    Last Post: 04-02-2013, 21:04

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •