    Alarm for flow activity when solenoid is off

    How can I code for flow activity in a rodi line if the neptune solenoid is in the OFF position? I want to get a heads up if the solenoid fails and water comes through the line. I have a 1/4 inch sensor on the line and im stuck because theres no "and" statements.

    This is what im hung on so far in the virtual outlet alarm I made:

    Set OFF
    Fallback OFF
    If RODI > 0.0 Then ON
    ??????????????

    I really want the "and" capability directly after the last command above, and would use it for: "AND outlet Solenoid = OFF"
    But theres no "and" - so how can this be done?

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Set OFF
    Fallback OFF
    If RODI > 0.0 Then ON
    If Outlet Solenoidname = ON Then OFF
    Defer 000:10 Then ON

    Do be warned that the flow meter won't sense a small trickle. It would need to go full blast on the RODI to not read zero with the 3gph minimum.

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    Regular Vistor Intel339's Avatar
    Join Date
    Mar 2015
    Location
    Frederick, MD
    Posts
    25
    Awesome. Full blast is better than nothing. This will be the 6th line of protection/ warning on my auto ato system.

Similar Threads

  1. Question: Flow sensor alarm.
    By Thaddias in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 7
    Last Post: 03-06-2023, 16:37
  2. Use Flow Sensor as an Alarm
    By myk5486 in forum Misc Apex Usage & Programming
    Replies: 3
    Last Post: 06-09-2020, 23:09
  3. Using flow sensor to shut off solenoid
    By willthiswork89 in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 3
    Last Post: 05-29-2020, 14:32
  4. Question: Return pump low flow alarm from FFM flow sensor
    By Cpage101 in forum APEX Fusion
    Replies: 3
    Last Post: 08-09-2019, 11:37
  5. Replies: 0
    Last Post: 06-28-2014, 11:44

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •