Thread: Co2 injection programming script help

  1. #1
    New User
    Join Date
    Jun 2015
    Location
    los angeles
    Posts
    2

    Co2 injection programming script help

    I was wondering If anybody can lend me a helping hand. I would like to create a program for my Co2 injected freshwater planted tank. Two different parameters for when my lights are on from 5am to 1pm and would like to have a range when the light are off. Is this the correct programming sequence for what I'm trying to achieve. My lights are not connected to the apex eb8 as I'm using the kessil controller.

    Fallback OFF
    If pHx2 < 6.40 Then OFF
    If pHx2 > 6.50 Then ON
    If Time 05:00 to 13:00 Then ON
    If pHx2 < 6.80 Then OFF
    If pHx2 > 6.90 Then ON
    If Time 13:00 to 05:00 Then ON

    Thanks for any advice,
    Jeff

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    No that will not work. The way apex programming works is that it goes from top to bottom and ignores any false statements. The last true statement wins.

    You have to create two virtual outlets to do this.

    Co2Day
    If pHx2 < 6.40 Then OFF
    If pHx2 > 6.50 Then ON
    If Time 13:00 to 05:00 Then OFF

    Co2Night
    If pHx2 < 6.80 Then OFF
    If pHx2 > 6.90 Then ON
    If Time 05:00 to 13:00 Then OFF

    Solenoid (physical outlet)
    Fallback OFF
    Set OFF
    If Outlet Co2Day = ON Then ON
    If Outlet Co2Night = ON Then ON

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    New User
    Join Date
    Jun 2015
    Location
    los angeles
    Posts
    2
    Thanks for responding zombie. Another question now to program a virtual outlet using an apex jr., my only choice to program one is through the apex display is that correct? Thanks in advance, Jeff

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by carmenjeff View Post
    Thanks for responding zombie. Another question now to program a virtual outlet using an apex jr., my only choice to program one is through the apex display is that correct? Thanks in advance, Jeff
    No you use the classic dashboard and add a DC4 or DC8 module to create 4 or 8 virtual outlets respectively. There is a sticky post on here explaining the process and the comprehensive manual explains it in great detail.

    You might be an engineer if...You have no life and can prove it mathematically.

Similar Threads

  1. Question: Programming for Co2
    By rduhb in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 6
    Last Post: 12-04-2019, 16:01
  2. need help with CO2 injection program
    By Morecowwbell in forum Misc Aquarium Automation Discussions
    Replies: 14
    Last Post: 03-02-2019, 06:40
  3. Programming for co2
    By lang510 in forum Misc Apex Usage & Programming
    Replies: 4
    Last Post: 03-12-2017, 11:53
  4. Question: CO2 Solenoid Plugged in to EB832 to Shut Off CO2 When PH Falls Too Low
    By SkyReef in forum Misc Apex Usage & Programming
    Replies: 4
    Last Post: 11-02-2016, 09:01
  5. Question: CO2 Solenoid Plugged in to EB832 to Shut Off CO2 When PH Falls Too Low
    By SkyReef in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 0
    Last Post: 08-13-2016, 19:24

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •