    Heater Outlet Turning off too early

    I have my Temp set to be between 77 and 78 degrees. My outlet turns on when it reaches below 77 degrees F. but it turns back off, rather than heating until 78 and shutting off. so basically its on at 76.9 off at 77. constantly. What in my programming is wrong?



    Fallback OFF
    Set OFF
    If Output New_Fish = ON Then ON
    If Temp > 78.0 Then OFF
    If Temp < 77.0 Then ON
    If Output Pumps_2_3 = OFF Then OFF
    If FeedA 000 Then OFF

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    You have to remove the set OFF if you want hysteresis.

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    New User
    Join Date
    Mar 2013
    Location
    32811
    Posts
    9
    Thank You Sir!

Similar Threads

  1. Issue with APEX turning co2 off early
    By kris2001 in forum Misc Apex Usage & Programming
    Replies: 1
    Last Post: 01-14-2022, 16:02
  2. Replies: 3
    Last Post: 04-19-2017, 18:41
  3. Question: Manually Turning ON an Outlet and Then automatically turning it OFF
    By cmeflygtp in forum Misc Apex Usage & Programming
    Replies: 4
    Last Post: 05-01-2016, 18:40
  4. Help! heater turning on and off to much
    By jrlamountain in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 31
    Last Post: 06-01-2015, 09:23
  5. Review My Program Lights keep turning off early
    By 09bumblebee in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 8
    Last Post: 05-04-2013, 21:49

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •