Set 50
Fallback OFF
If FeedA 010 Then 20
If Output mainpump = OFF Then OFF
Defer 001:00 Then ON
I want to set it at 50% and go down to 20% when I feed. I want it to turn back up to 50% when the feed time runs out. Does this work?
Set 50
Fallback OFF
If FeedA 010 Then 20
If Output mainpump = OFF Then OFF
Defer 001:00 Then ON
I want to set it at 50% and go down to 20% when I feed. I want it to turn back up to 50% when the feed time runs out. Does this work?
Technically yes, but note that the quick jump to and from full intensity to feed intensity can reduce motor life on some but not all 0-10V pumps. If that at all concerns you, use ramp profiles instead of percentages.
You might be an engineer if...You have no life and can prove it mathematically.
Thank you, Zombie.
I created a virtual profile for my skimmer and added it into my feed code.
Set 60
Fallback OFF
If FeedA 010 Then skmr_feed
If Output mainpump = OFF Then OFF
Defer 001:00 Then ON
Screen Shot 2018-02-05 at 7.15.37 PM.png
What do you think?
You actually want two. Instead of using 60 for set make a profile with a ramp 1 minute start 20 end 60. Your skim feed is backwards. You want 60 start and 20 end. This way when you reboot the system or end the feed, it will slowly ramp up from 20 to 60 and when you feed it will slowly ramp down from 60 to 20.
You might be an engineer if...You have no life and can prove it mathematically.
You would place like this
Fallback OFF
Set rampup
If FeedA 010 Then rampdown
If Output mainpump = OFF Then OFF
Defer 001:00 Then ON
You might be an engineer if...You have no life and can prove it mathematically.
The physical energy bar outlet should just be:
Fallback ON
Set ON
Or you could just plug it into the wall too.