    Turning off Heater during Water change

    This is my first week of using Apex so please bare with me.

    I have my water change set on FeedD. I’m turning off everything in my sump including my heaters. Sw3bot is my fail safe float if the water levels get low in my sump.

    (Heater1 and Heater2 Code)

    Fallback OFF
    If Tmp < 78 Then ON
    If Tmp > 78.5 Then OFF
    If Sw3Bot CLOSED Then OFF
    If FeedD 030 Then OFF

    1st question, if I start FeedD and the temp is below 78 will my Heater still come on? When does Apex stop reading the code if there are more than one value that is True?

    2nd Question. Is having a .5 F range ok or should I widen the on and off range between temperatures? Ie: 78 to 79

    Thanks


    Sent from my iPad using Tapatalk

  2. #2
    Frequent Visitor
    Join Date
    Jan 2016
    Location
    Cincinnati, ohio
    Posts
    709
    I also is a .5 degree difference, so that should be fine.

    apex evaluates the entire code continuously. The order of the code is important as the last true statement wins. In your example feedD will always result in the unit being off. However if the if temp < 78 then on were last it would be on even of feedD is active.

  3. #3
    Regular Vistor
    Join Date
    Feb 2018
    Location
    Louisiana
    Posts
    30
    Quote Originally Posted by Frogfish View Post
    I also is a .5 degree difference, so that should be fine.

    apex evaluates the entire code continuously. The order of the code is important as the last true statement wins. In your example feedD will always result in the unit being off. However if the if temp < 78 then on were last it would be on even of feedD is active.
    Thank you for the help


    Sent from my iPad using Tapatalk

  4. #4
    Frequent Visitor Todd's Avatar
    Join Date
    Jan 2013
    Location
    Huntsville, AL
    Posts
    583
    Quote Originally Posted by Iansu View Post

    When does Apex stop reading the code if there are more than one value that is True?
    The Apex reads all commands top to bottom. Any FALSE conditions are ignored. The last TRUE condition prevails. So, in your current code, while FeedD plus additional 30 minutes is ON(TRUE), the outlet will remain OFF regardless of any previous conditions. The general approach to programming is to define the default/nominal behavior and then add exceptions/overrides.

Similar Threads

  1. DOS clicking + different run times per side during automatic water change + water change frequency
    By reefdiver in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 1
    Last Post: 07-24-2021, 07:26
  2. Help! DOS for auto water change, ATK adding water while water Change takes place
    By Tundra in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 6
    Last Post: 09-14-2020, 10:54
  3. Question: Auto water change & Manual Water Change
    By mebeknob in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 3
    Last Post: 03-10-2020, 14:43
  4. DOS Water change not delivering the correct amount of water
    By Vassallo73 in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 6
    Last Post: 06-01-2019, 22:57
  5. Question: turning off auto refill while doing water change.
    By bhbbhb in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 4
    Last Post: 07-27-2015, 13:50

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •