    Manual ATO using 2 Solenoids

    I'm a beginner with the apex system. I currently have my RODI system piped directly into the sump I supply top off water manually with a valve. I have 2 24v apex solenoids pipe inline from RODI to the sump. I would like to set up a program to open both solenoids for a predetermined amount of time then close them both. Can i set it up like a feed mode with a button? Eventually I want it to work with an optical sensor to make it a fully automated ATO in the futureIMG_20180225_151224038.jpg.

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    Yes, you can do it with a Feed cycle. Pick one of the 4 Feed cycles (A, B, C, or D), then set the Feed? Interval for that Feed cycle to the length of time (in minutes) you want to use. You do this on the Misc settings page using either APEX Local or APEX Fusion. Let's say you use FeedB and want the top-off process to last 15 minutes. Use 15 in the FeedB Interval, then program one solenoid output like this:
    [Solenoid1]
    Fallback OFF
    Set OFF
    If FeedB 000 Then ON

    The second solenoid may be programmed exactly the same, or you can make it mirror the ON/OFF state of Solenoid1, like this:
    [Solenoid2]
    Fallback OFF
    Set OFF
    If Output Solenoid1 = ON Then ON

    There's no functional difference between the two.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    New User
    Join Date
    Jan 2018
    Location
    Sparks NV
    Posts
    9
    Thank You very much! I was able to increase the time on my feed cycle B. This would be my first time programing could you point to a beginners guide to programing? Would I copy what you have listed under solenoid 1 into the configuration for Solenoid #1?

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Nicksreef View Post
    Thank You very much! I was able to increase the time on my feed cycle B. This would be my first time programing could you point to a beginners guide to programing? Would I copy what you have listed under solenoid 1 into the configuration for Solenoid #1?
    Feed cycle length is in misc setup.

    I would not copy the code from solenoid 1 to solenoid 2. Use the code he gave but change the name in the code to whatever you actually named solenoid 1. This way if you need to change the code, you only have to edit solenoid 1 instead of both.

    You might be an engineer if...You have no life and can prove it mathematically.

Similar Threads

  1. Review My Program ATO VO for Manual Water Change
    By crs751 in forum Misc Apex Usage & Programming
    Replies: 5
    Last Post: 07-20-2020, 16:19
  2. Topping off ATO using Solenoids and Optic Sensors
    By Castris in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 0
    Last Post: 04-16-2019, 13:34
  3. ATO with Kalk Reactor and Solenoids
    By tamn3 in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 4
    Last Post: 07-04-2018, 21:48
  4. Using DOS as a manual ATO
    By versaquatics in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 6
    Last Post: 01-30-2018, 15:38
  5. Manual ATO question
    By adamsb in forum Misc Apex Usage & Programming
    Replies: 7
    Last Post: 05-07-2015, 13:12

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •