    Different delays for skimmer startup

    I don't feed the corals every day, but I do feed the fish every day.

    I have feed mode A set to 6 minutes, with a 5 minute "defer" statement in the program for the skimmer. Feed mode B is set to 10 minutes (so I can target feed), but I want the skimmer delay set to 30 minutes so the food can recirculate and the corals can filter feed.

    How can I set that outlet up? I set the "If Feed mode A 005 then off" but it turns right back on. If I set a different "defer," it defaults to the longest one regardless of the feed mode selected. I set the defers to 5:00 on all the outlets for the time being.

    Fallback ON
    Set ON
    If FeedA 000 Then OFF
    Defer 005:00 Then ON
    If FeedB 000 Then OFF
    Defer 030:00 Then ON
    If FeedC 000 Then OFF
    Defer 005:00 Then ON
    If FeedD 000 Then OFF
    Defer 005:00 Then ON

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    You want this. You can delete any feed lines (except B) If you have them in your return pump code. If you have a high level float or optical, you also want to add a line to turn off when that is high.

    Fallback ON
    Set ON
    If Output ReturnName = OFF Then OFF
    If Power Apex Off 001 Then OFF
    If FeedA 000 Then OFF
    If FeedB 025 Then OFF
    If FeedC 000 Then OFF
    If FeedD 000 Then OFF
    Defer 005:00 Then ON



    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    Regular Vistor
    Join Date
    Apr 2017
    Location
    Boston, MA
    Posts
    26
    Quote Originally Posted by zombie View Post
    You want this. You can delete any feed lines (except B) If you have them in your return pump code. If you have a high level float or optical, you also want to add a line to turn off when that is high.

    Fallback ON
    Set ON
    If Output ReturnName = OFF Then OFF
    If Power Apex Off 001 Then OFF
    If FeedA 000 Then OFF
    If FeedB 025 Then OFF
    If FeedC 000 Then OFF
    If FeedD 000 Then OFF
    Defer 005:00 Then ON



    You might be an engineer if...You have no life and can prove it mathematically.
    Why do I need the output return name and the power line?

  4. #4
    Frequent Visitor Todd's Avatar
    Join Date
    Jan 2013
    Location
    Huntsville, AL
    Posts
    583
    Implicit in zombies recommendation is that Defer applies to the entire outlet, not the preceding line of code. So one Defer for ON and another for OFF (if needed) per outlet. I prefer to place them at the end even though it is not required.

    The pump outlet check assumes your skimmer is in a sump and will overflow when the pump is shut off. Same with the power check, assumes you will want an extra delay when power is restored. It gives it time to boot up.

  5. #5
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,488
    zombie assumes that you have an in-sump skimmer, which generally are quite sensitive to the water level in the sump and will overflow if the water level is high. The If Output line ties the operation of the skimmer to that of the return pump. If the return pump is OFF, so will be the skimmer. The If Power line forces the skimmer to stay off briefly after a power outage or Apex reboot. The Defer line adds 5 minutes of delay to skimmer startup to allow time for the water in the sump to normalize, and this applies across the board - if the return pump was off then is turned on again or the Apex has restarted, the Defer delays the skimmer startup by 5 minutes.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  6. #6
    Regular Vistor
    Join Date
    Apr 2017
    Location
    Boston, MA
    Posts
    26
    Quote Originally Posted by Todd View Post
    Implicit in zombies recommendation is that Defer applies to the entire outlet, not the preceding line of code. So one Defer for ON and another for OFF (if needed) per outlet. I prefer to place them at the end even though it is not required.

    The pump outlet check assumes your skimmer is in a sump and will overflow when the pump is shut off. Same with the power check, assumes you will want an extra delay when power is restored. It gives it time to boot up.
    Ok, I am using this on a AIO with a battery backup so power outages are not too important.

    So the 5 minute Defer at the end is added into all the times. So feed mode A is 000, but is actually 5 minutes because of the Defer.

    B is 30 minutes 25+5.

    Correct?

  7. #7
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Yes. The defer applies globally so it will stay off an extra 5 minutes for any condition that turns it off.

    You might be an engineer if...You have no life and can prove it mathematically.

  8. #8
    Frequent Visitor Todd's Avatar
    Join Date
    Jan 2013
    Location
    Huntsville, AL
    Posts
    583
    Just to be clear, there is a configured duration for each feed cycle. The 000 parameter adds additional time, as well as the defer. So for example, FeedA 010 would be the duration of FeedA + 10 minutes, plus length of Defer if present. In the classic dashboard, Feed durations are under Configuration>Misc Setup.

  9. #9
    Regular Vistor
    Join Date
    Apr 2017
    Location
    Boston, MA
    Posts
    26
    Quote Originally Posted by zombie View Post
    Yes. The defer applies globally so it will stay off an extra 5 minutes for any condition that turns it off.

    You might be an engineer if...You have no life and can prove it mathematically.
    Ok, this is my issue. I have set it up this way before and it doesn't work. Feed B still turns the skimmer on after 5 minutes.

    I'll have to try to program it via the display panel. Maybe it's fusion

  10. #10
    Regular Vistor
    Join Date
    Apr 2017
    Location
    Boston, MA
    Posts
    26
    Quote Originally Posted by zombie View Post
    Yes. The defer applies globally so it will stay off an extra 5 minutes for any condition that turns it off.

    You might be an engineer if...You have no life and can prove it mathematically.
    Nope, still doesn't work. Even after using the display module.

    Very fustrating.

  11. #11
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Did you cancel the feed timer? If you did then it will turn on 5 minutes later. It will only do the extra 25 minutes if you let the feed timer expire.

    You might be an engineer if...You have no life and can prove it mathematically.

Similar Threads

  1. Help with first time startup
    By MCHammerTime in forum Apex Classic Dashboard
    Replies: 8
    Last Post: 04-30-2020, 05:52
  2. Skimmer delay on startup
    By sjhart in forum Misc Apex Usage & Programming
    Replies: 14
    Last Post: 07-27-2018, 18:13
  3. AFS, Feed buttons and pump delays
    By 6check in forum APEX Fusion
    Replies: 7
    Last Post: 05-30-2018, 16:38
  4. How to set up different delays for same outlet
    By joeyrm in forum Misc Apex Usage & Programming
    Replies: 2
    Last Post: 12-07-2016, 21:56
  5. Read This First! Where to download the startup CD if you've lost it
    By aquamanic in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 0
    Last Post: 11-10-2013, 14:53

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •