There is a 30 sec to a couple minute refresh period for fusion and if it shows disconnected, don't consider any states up to date.
The if Error line means the pump ran longer than 3 minutes on a single fill and it currently in manual OFF as a safeguard.
Your code looks fine. 3 minutes should be reasonable since it can't compound through successive doses, but test it to find out. Let the pump run for up to 3 minutes, time it and if the water level raises a significant amount (like all the way from the low to high switch) then stop the timer and use that time. Best practice is between 1.5 to 3 times the longest fill in a 1-2 day test period.