    FMM module on my ATK just keeps clicking

    Just got back from vacation after a week of errors from my ATK . The FMM module just keeps clicking and the ATK hasn’t worked for over a week now . Thank god for some friends that were able to stop over and top off the tank .
    Got back last night and tried to reset and also update the FMM and still nothing . Is my FMM bad ?

    Programming hasn’t changed -
    Fallback OFF
    Set OFF
    If Swx8_1 OPEN Then ON
    If Swx8_2 CLOSED Then OFF
    When On > 030:00 Then OFF
    Defer 000:10 Then ON
    Defer 000:04 Then OFF
    Min Time 060:00 Then OFF

    Any ideas ?

  2. #2
    New User odietel's Avatar
    Join Date
    Feb 2014
    Location
    Rosendale, Wi
    Posts
    7
    Unplugged the pmup and the clicking stops . I’m assuming the pump is bad ?


    Sent from my iPhone using Tapatalk

  3. #3
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    Bad pmup would be my first guess. Unfortunately does not seem to be that rare, so I keep a spare one on hand.

  4. #4
    NSI Member
    Join Date
    Jan 2013
    Location
    MN
    Posts
    2,565
    Bad PMUP caused the same behavior for me. Most likely what's happening with yours. If you are still in warranty contact support. Otherwise I would go with some other pump.

  5. #5
    Frequent Visitor
    Join Date
    May 2017
    Location
    Minneapolis, MN (CST)
    Posts
    220
    Ditto the above comments. What may be happening is the pump is drawing too much current and the over-current protection in the FMM is shutting it off, then it’s trying to turn on only to have the same thing happen again.

Similar Threads

  1. Can the DC24 on EB832 power the ATK (FMM) module?
    By Chris155hp in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 14
    Last Post: 02-04-2023, 07:53
  2. Does Neptune sell the ATK accessories without the FMM module
    By Allentown in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 2
    Last Post: 11-26-2021, 00:31
  3. Review My Program FMM module and ATK pump
    By asulistyo in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 3
    Last Post: 11-04-2020, 00:05
  4. FMM Module Clicking
    By Reefman in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 9
    Last Post: 02-11-2018, 12:50
  5. Question: New ATK/FMM module and issues
    By CaraRichman in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 1
    Last Post: 12-12-2017, 14:08

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •