I added a VO to my ATO programming to turn off the ATO during a manual water change. After I added this line of code I noticed that my ATO wasn't on when the sump fill float was closed. I'm certain I have something out of sequence. My code is as follows:
Fallback OFF
Set OFF
If SmpFil CLOSED Then ON
If SmpHI OPEN Then OFF
When On > 008:00 Then OFF
If T_Salt < 33.0 Then OFF
If Output Water_Cng = ON Then OFF
Defer 010:00 Then ON
Please correct or advise what I'm doing wrong. And please let me know what the order is that I need to follow when programming the Apex. Thanks.