    1" flow monitor reading 1300 + with a mag drive 7 return pump.

    I can't get my flow monitor to read correctly. It's constantly reading between 1300 and 1400 gph. I know it's no where near the 250-400 the mag 7 is pushing. Any thoughts on getting it to read correctly?

    Sent from my FRD-L04 using Tapatalk

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,488
    I suspect that your FMM is set to display flow values in LPH, not GPH. Using the Classic Dashboard, go to the Module Setup page, select the FMM, and check that setting.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,488
    Also, check that the flow sensor is set to 1”, not 2” in the same place.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  4. #4
    New User
    Join Date
    Apr 2018
    Location
    St Thomas usvi
    Posts
    12
    Thanks. I'll check it when I get home from work and let you know.

    Sent from my FRD-L04 using Tapatalk

  5. #5
    New User
    Join Date
    Apr 2018
    Location
    St Thomas usvi
    Posts
    12
    Quote Originally Posted by fishybizzness View Post
    Thanks. I'll check it when I get home from work and let you know.

    Sent from my FRD-L04 using Tapatalk
    How do I do it in fusion? I can't get the classic to load on my tablet and it doesn't give me the option on my phone.. thanks

    Sent from my FRD-L04 using Tapatalk

  6. #6
    New User
    Join Date
    Apr 2018
    Location
    St Thomas usvi
    Posts
    12
    Quote Originally Posted by RussM View Post
    Also, check that the flow sensor is set to 1”, not 2” in the same place.
    How do I do it in fusion? I can't get the classic to load on my tablet and it doesn't give me the option on my phone.. thanks

    Sent from my FRD-L04 using Tapatalk

  7. #7
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by fishybizzness View Post
    How do I do it in fusion? I can't get the classic to load on my tablet and it doesn't give me the option on my phone.. thanks

    Sent from my FRD-L04 using Tapatalk
    Tablets and phones don't work well with the classic dashboard. You need to use a computer or a Bluetooth keyboard and mouse if a laptop or desktop isn't an option. Touch controls don't play nice with the classic dashboard.

    You might be an engineer if...You have no life and can prove it mathematically.

  8. #8
    New User
    Join Date
    Apr 2018
    Location
    St Thomas usvi
    Posts
    12
    Quote Originally Posted by zombie View Post
    Tablets and phones don't work well with the classic dashboard. You need to use a computer or a Bluetooth keyboard and mouse if a laptop or desktop isn't an option. Touch controls don't play nice with the classic dashboard.

    You might be an engineer if...You have no life and can prove it mathematically.
    Thanks for the quick reply. I have a blue tooth keyboard for the tablet but I can only get to the main screen. I can't get further than this.

    Sent from my FRD-L04 using Tapatalk

  9. #9
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    You need to type the ip address of the apex into a browser. That is the android app which does not have any of the options you are looking for.

    You might be an engineer if...You have no life and can prove it mathematically.

  10. #10
    New User
    Join Date
    Apr 2018
    Location
    St Thomas usvi
    Posts
    12
    Quote Originally Posted by zombie View Post
    You need to type the ip address of the apex into a browser. That is the android app which does not have any of the options you are looking for.

    You might be an engineer if...You have no life and can prove it mathematically.
    I got it done! I thank you immensly!! That's been driving me nuts! You're a rock star!!?

    Sent from my FRD-L04 using Tapatalk

Similar Threads

  1. 1/4" flow settings no reading
    By Houm in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 11
    Last Post: 12-01-2022, 09:26
  2. Big pump 1.25" 2000gph... Flow sensor 2" 3k GPH? How to maximize this?
    By FrozenWater in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 2
    Last Post: 06-03-2020, 21:07
  3. Question: Return pump low flow alarm from FFM flow sensor
    By Cpage101 in forum APEX Fusion
    Replies: 3
    Last Post: 08-09-2019, 11:37
  4. Question: Flow sensor question: I'm using 3/4" PVC for return. Should I step down to 1/2" sensor, or step up to 1" sensor?
    By smartwater101 in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 1
    Last Post: 04-04-2019, 13:31
  5. 1/2" flow sensor seems to be reading very low.
    By powers2001 in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 2
    Last Post: 09-22-2017, 05:06

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •