    Heater 'Stuck' in on position

    I have a 'Schego' heater controlled by my Apex. Everything has been fine since install around 18 months ago.
    These are my settings

    Fallback OFF
    If TEMP < 26.0 Then ON
    If TEMP > 27.0 Then OFF

    Its in the outlet 4.5 of a 6 bar setup (im in the UK)
    It went up to 32 yesterday evening and I have lost fish & corals.

    Did a reset and checked all but its still exceeding 27 gradually and does not turn off.

    Any assistance greatly appreciated

  2. #2
    Frequent Visitor
    Join Date
    Nov 2015
    Location
    Duluth, GA
    Posts
    163
    Sorry to hear you lost livestock.

    Have you tried the heater in a different outlet?
    Maybe the relay for that outlet is bad.

    Another thing you can do is turn logging on for that outlet and see that Apex is trying to turn it off at your set temp.

    Sent from my SM-G955U using Tapatalk

  3. #3
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by anit77 View Post
    Sorry to hear you lost livestock.

    Have you tried the heater in a different outlet?
    Maybe the relay for that outlet is bad.

    Another thing you can do is turn logging on for that outlet and see that Apex is trying to turn it off at your set temp.

    Sent from my SM-G955U using Tapatalk
    Thanks for your response
    I have tried another outlet but with the same result. The 'Log' is enabled but how do you check to see if Apex is trying to turn it off?

  4. #4
    Frequent Visitor
    Join Date
    Nov 2015
    Location
    Duluth, GA
    Posts
    163
    Check the log in Fusion.

    Sent from my SM-G955U using Tapatalk

  5. #5
    Frequent Visitor
    Join Date
    Nov 2015
    Location
    Duluth, GA
    Posts
    163
    Setting a Temp alarm is also a good idea.

    If Temp < 27.2 Then On

    This will alert you of the temp getting too high before it causes problems.

    Sent from my SM-G955U using Tapatalk

  6. #6
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by anit77 View Post
    Setting a Temp alarm is also a good idea.

    If Temp < 27.2 Then On

    This will alert you of the temp getting too high before it causes problems.

    Sent from my SM-G955U using Tapatalk
    Again, I appreciate your response. In the Output Log in Apex Fusion there is a sequence of 'OFF' & 'ON'. The latest is just over 45 minutes ago when its in the 'OFF' state but why am I seeing the small orange 'ON' sign on the tiled display plus the temperature is increasing?? Main tile is set to 'AUTO'

  7. #7
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,464
    Quote Originally Posted by anit77 View Post

    If Temp < 27.2 Then On

    This will alert you of the temp getting too high before it causes problems.
    This should use a greater than sign (>)
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  8. #8
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by RussM View Post
    This should use a greater than sign (>)
    Ok, just a 1 line command set exactly as that but getting nothing even though temp currently shows 27.3

  9. #9
    Frequent Visitor
    Join Date
    Nov 2015
    Location
    Duluth, GA
    Posts
    163
    Sorry about the <... was drinking my 1st cup of coffee.

    Is your email alert setup correctly and in the auto position?

    Sent from my SM-G955U using Tapatalk

  10. #10
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by anit77 View Post
    Sorry about the <... was drinking my 1st cup of coffee.

    Is your email alert setup correctly and in the auto position?

    Sent from my SM-G955U using Tapatalk
    Yes, just sent myself a test email to make sure was configured correctly.
    Its still 27.3..no email warning and the output log is showing 'OFF' so I would have thought the temperature would have decreased slightly? Also do you know why the orange 'On' indicator is on the tile...now 27.4 as I write

  11. #11
    Frequent Visitor
    Join Date
    Nov 2015
    Location
    Duluth, GA
    Posts
    163
    Is there an indicator light in the heater and if so is it on?

    Can you post a screen shot of the outlet programming?

    Sent from my SM-G955U using Tapatalk

  12. #12
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    IMG_3968.jpgIMG_3969.jpgIMG_3970.jpg
    Quote Originally Posted by anit77 View Post
    Is there an indicator light in the heater and if so is it on?

    Can you post a screen shot of the outlet programming?

    Sent from my SM-G955U using Tapatalk

  13. #13
    Frequent Visitor
    Join Date
    Nov 2015
    Location
    Duluth, GA
    Posts
    163
    Everything looks right except the output showing on. The log shows the unit turning off that output almost immediately after turning it on.

    What about the indicator light on the heater itself and/or trying another heater?

    Does the heater have it's own thermostat and have you restarted the Apex.

    The heater could be bad or the relay could be sticking. @RussM

    Sent from my SM-G955U using Tapatalk

  14. #14
    Frequent Visitor
    Join Date
    Mar 2015
    Location
    San Jose,CA
    Posts
    528
    Look in your inputs page.

    Do you have another input with the same name?

    Do you have another outlet with the same name?


    Sent from my iPhone using Tapatalk

  15. #15
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by anit77 View Post
    Everything looks right except the output showing on. The log shows the unit turning off that output almost immediately after turning it on.

    What about the indicator light on the heater itself and/or trying another heater?

    Does the heater have it's own thermostat and have you restarted the Apex.

    The heater could be bad or the relay could be sticking. @RussM

    Sent from my SM-G955U using Tapatalk
    The heater has no thermostat or indicator. Its a titanium model by Schego. It currently feels hot to the touch

  16. #16
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by vhuang168 View Post
    Look in your inputs page.

    Do you have another input with the same name?

    Do you have another outlet with the same name?


    Sent from my iPhone using Tapatalk
    No, is the answer to both questions...now 27.5 and no email alert either. Im going to have to turn it off soon...i really dont know what to do next?

  17. #17
    Frequent Visitor
    Join Date
    Nov 2015
    Location
    Duluth, GA
    Posts
    163
    We all want our Apex to be the be all end all for controlling our tanks but you really need to have redundancies setup for critical components. With heaters, if they don't come with their own thermostat you should add one and set it slightly higher than the Apex. This way if something goes wrong the thermostat will shutdown the heater.

    Have you restarted the Apex yet?

    Sent from my SM-G955U using Tapatalk

  18. #18
    Frequent Visitor
    Join Date
    Mar 2015
    Location
    San Jose,CA
    Posts
    528
    Email outlet programming?

    Try renaming that probe and changing the programming to match then restarting the Apex.


    Sent from my iPhone using Tapatalk

  19. #19
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by anit77 View Post
    We all want our Apex to be the be all end all for controlling our tanks but you really need to have redundancies setup for critical components. With heaters, if they don't come with their own thermostat you should add one and set it slightly higher than the Apex. This way if something goes wrong the thermostat will shutdown the heater.

    Have you restarted the Apex yet?

    Sent from my SM-G955U using Tapatalk
    Yes, restarted but noticed the green 'Status' lights did not go out. did a hard reset by removing plugs from 1 link and Apex

  20. #20
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by redseareg View Post
    Yes, restarted but noticed the green 'Status' lights did not go out. did a hard reset by removing plugs from 1 link and Apex
    thermostat you should add one and set it slightly higher than the Apex. This way if something goes wrong the thermostat will shutdown the heater.

    How does that help with the heater without a thermostat?

  21. #21
    Frequent Visitor
    Join Date
    Nov 2015
    Location
    Duluth, GA
    Posts
    163
    Quote Originally Posted by redseareg View Post
    How does that help with the heater without a thermostat?
    https://www.bulkreefsupply.com/therm...caAsj1EALw_wcB

    Anything similar and available locally to you would be good to add.

    Sent from my SM-G955U using Tapatalk

  22. #22
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by anit77 View Post
    https://www.bulkreefsupply.com/therm...caAsj1EALw_wcB

    Anything similar and available locally to you would be good to add.

    Sent from my SM-G955U using Tapatalk
    At approaching 5pm on a Sunday nowhere open now

  23. #23
    Regular Vistor
    Join Date
    Jul 2016
    Location
    London, UK
    Posts
    27
    Quote Originally Posted by vhuang168 View Post
    Email outlet programming?

    Try renaming that probe and changing the programming to match then restarting the Apex.


    Sent from my iPhone using Tapatalk
    In the Apex classic page I have 2 Probe/Input One is 'TEMP-tmp' one is 'TEMP - TmpX5 and the other is 'TEMP_Flo_6

    Email alert is set as 'If TEMP (is greater to) 27.2 Then ON' and the tile is set to Auto

  24. #24
    Frequent Visitor
    Join Date
    Mar 2015
    Location
    San Jose,CA
    Posts
    528
    So the answer to my previous question was yes.

    You have 2 inputs named TEMP.

    Where is your temp probe connected to?

    Change the other one to something else.


    Sent from my iPhone using Tapatalk

  25. #25
    Frequent Visitor
    Join Date
    Nov 2015
    Location
    Duluth, GA
    Posts
    163
    Quote Originally Posted by vhuang168 View Post
    Email outlet programming?

    Try renaming that probe and changing the programming to match then restarting the Apex.


    Sent from my iPhone using Tapatalk
    Have you tried this above?

    If you plug something else into that outlet like a simple light and set it manually on and off (not auto) and the light turns on and off then there's nothing wrong with the relay in the EB.

    After trying the above recommendation and there's still a problem and you know the relay is good then there must be some corruption in the base. Have you added anything new or done any different programming before this started?

    The way to correct corruption is to factory reset by memory init all in misc settings, reflash the firmware & webpages and then reprogramming everything from scratch. This should be a last resort. You should start a ticket with Neptune immediately.

    Lastly do you have a backup heater with a thermostat? If not do you have a local reefer friend that can loan you one?

    *EDIT* Cross post. I see you have two probes named temp...

    Sent from my SM-G955U using Tapatalk

Page 1 of 3 123 LastLast

Similar Threads

  1. Question: Warning for DOS in ON or OFF Position
    By MBLang in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 1
    Last Post: 05-03-2021, 09:08
  2. ATO Sensor stuck in the closed position
    By Andruw91 in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 15
    Last Post: 11-01-2020, 16:50
  3. Heater stuck on after a slight change
    By Dave.mrnk in forum Apex Programming for Heaters and Chillers
    Replies: 13
    Last Post: 12-08-2018, 15:14
  4. New AFS Stuck in open position
    By Jballauer in forum Misc Apex Usage & Programming
    Replies: 5
    Last Post: 06-18-2015, 10:27
  5. Auto feeder position
    By TheThingIs in forum Apex Installation and Mounting
    Replies: 3
    Last Post: 06-26-2014, 05:37

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •