    How to ramp up a pump when its turned back to AUTO

    I have a powerful return pump and when I turn it back to auto after I have had it turned off it goes straight to 100%. It is controllable via a 0-10V port.

    How can I get it to slowly ramp up when its switched back to auto as opposed to it going straight to maximum. Basically a soft start

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Create a profile that ramps from 0 to 100 over 1 minute. Then instead of using ON, replace it with the profile name.

    You might be an engineer if...You have no life and can prove it mathematically.

  3. #3
    Frequent Visitor
    Join Date
    Jul 2015
    Location
    Dubai, UAE
    Posts
    89
    Another good idea...thank you

  4. #4
    Frequent Visitor
    Join Date
    Jul 2015
    Location
    Dubai, UAE
    Posts
    89
    Sorry, I'm still new to this...
    I have made a profile RtnRmpUp (a profile is like a function in normal programming?)

    How do I call it from the RtnOn-Off outlet

    I tried

    If Output RtnOn-Off =On Then RtnRampUp

    But it didnt work

  5. #5
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    What is your current program for the 0-10V output?

    You might be an engineer if...You have no life and can prove it mathematically.

  6. #6
    Frequent Visitor
    Join Date
    Jul 2015
    Location
    Dubai, UAE
    Posts
    89
    On Variable outlet 3 I have the following. It just ramps the return pump down for a few minutes at each feeding

    Fallback ON
    tdata 00:00:00,0,0,100,0,0,0,0,0,0,0,0,0,0
    tdata 07:55:00,0,0,100,0,0,0,0,0,0,0,0,0,0
    tdata 08:00:00,0,0,10,0,0,0,0,0,0,0,0,0,0
    tdata 08:05:00,0,0,10,0,0,0,0,0,0,0,0,0,0
    tdata 08:10:00,0,0,100,0,0,0,0,0,0,0,0,0,0
    tdata 11:55:00,0,0,100,0,0,0,0,0,0,0,0,0,0
    tdata 12:00:00,0,0,10,0,0,0,0,0,0,0,0,0,0
    tdata 12:05:00,0,0,10,0,0,0,0,0,0,0,0,0,0
    tdata 12:10:00,0,0,100,0,0,0,0,0,0,0,0,0,0
    tdata 15:55:00,0,0,100,0,0,0,0,0,0,0,0,0,0
    tdata 16:00:00,0,0,10,0,0,0,0,0,0,0,0,0,0
    tdata 16:05:00,0,0,10,0,0,0,0,0,0,0,0,0,0
    tdata 16:10:00,0,0,100,0,0,0,0,0,0,0,0,0,0
    tdata 19:55:00,0,0,100,0,0,0,0,0,0,0,0,0,0
    tdata 20:00:00,0,0,10,0,0,0,0,0,0,0,0,0,0
    tdata 20:05:00,0,0,10,0,0,0,0,0,0,0,0,0,0
    tdata 20:10:00,0,0,100,0,0,0,0,0,0,0,0,0,0
    tdata 23:59:00,0,0,100,0,0,0,0,0,0,0,0,0,0

  7. #7
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    That's not the recommended approach. Search vFeed to see how to link the return to your feeder properly, but you should have something along the lines of this.

    Fallback ON
    Set RampUp
    If Output vFeed = ON Then OFF


    You might be an engineer if...You have no life and can prove it mathematically.

  8. #8
    Frequent Visitor
    Join Date
    Jul 2015
    Location
    Dubai, UAE
    Posts
    89
    Would this work?

    Return Pump:

    Fallback On
    Set On
    If Outlet VFEEDOFF=On Then Off



    Feeder:

    Set OFF
    If Output VFEEDOFF = ON Then ON
    Defer 001:00 Then ON

    Profile:
    RtnRampUp

    Time:1
    Start intensity=0
    End intensity=100

    Outlet:
    VFEEDOFF

    Set OFF
    If Time 08:00 to 08:04 Then ON
    If Time 12:00 to 12:04 Then ON
    If Time 16:00 to 16:04 Then ON
    If Time 20:00 to 20:04 Then ON
    Defer 04:00 Then RtnRampUp

  9. #9
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    No, but this will

    Return Pump (0-10V)

    Fallback On
    Set RtnRampUp
    If Outlet VFEEDOFF=On Then Off



    Feeder:

    Set OFF
    If Output VFEEDOFF = ON Then ON
    Defer 001:00 Then ON

    Profile:
    RtnRampUp

    Time:1
    Start intensity=0
    End intensity=100

    Outlet:
    VFEEDOFF

    Set OFF
    If Time 08:00 to 08:04 Then ON
    If Time 12:00 to 12:04 Then ON
    If Time 16:00 to 16:04 Then ON
    If Time 20:00 to 20:04 Then ON




    You might be an engineer if...You have no life and can prove it mathematically.

  10. #10
    Frequent Visitor
    Join Date
    Jul 2015
    Location
    Dubai, UAE
    Posts
    89
    Thanks very much for your help

    I didn't like the sudden switch off of the pump and that at 0 it allowed a back syphon through the return outlet. The back syphon introduced air bubbles when the return pump ramped back up so I adjusted by adding a further profile to ramp down to the pumps stall point (in my case 6%), thus preventing the syphon and air.

    RtnRampDwn
    Time 1
    Start Intensity=6%
    End Intensity=100%

    I adjusted the RtnRampUp
    Time 1
    Start Intensity=6%
    End Intensity=100%

    I changed Return-pump

    Fallback ON
    Set RtnRampUp
    If Output vFeedoff = ON Then RtnRampDwn (gradual ramp down of return to stall point)
    If Leak CLOSED Then OFF (turn return off if leak detected)

    I added Feed A to the VFeedOff virtual outlet to allow for manual feeding.

    Set OFF
    If Time 08:00 to 08:04 Then ON
    If Time 12:00 to 12:04 Then ON
    If Time 16:00 to 16:04 Then ON
    If Time 20:00 to 20:04 Then ON
    If FeedA 000 Then ON (allow for manual feed)



  11. #11
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Batty View Post
    Thanks very much for your help

    I didn't like the sudden switch off of the pump and that at 0 it allowed a back syphon through the return outlet. The back syphon introduced air bubbles when the return pump ramped back up so I adjusted by adding a further profile to ramp down to the pumps stall point (in my case 6%), thus preventing the syphon and air.

    RtnRampDwn
    Time 1
    Start Intensity=6%
    End Intensity=100%

    I adjusted the RtnRampUp
    Time 1
    Start Intensity=6%
    End Intensity=100%

    I changed Return-pump

    Fallback ON
    Set RtnRampUp
    If Output vFeedoff = ON Then RtnRampDwn (gradual ramp down of return to stall point)
    If Leak CLOSED Then OFF (turn return off if leak detected)

    I added Feed A to the VFeedOff virtual outlet to allow for manual feeding.

    Set OFF
    If Time 08:00 to 08:04 Then ON
    If Time 12:00 to 12:04 Then ON
    If Time 16:00 to 16:04 Then ON
    If Time 20:00 to 20:04 Then ON
    If FeedA 000 Then ON (allow for manual feed)


    Think you got a typo on ramp down. Looks like your min and max are swapped.

    You might be an engineer if...You have no life and can prove it mathematically.

  12. #12
    Frequent Visitor
    Join Date
    Jul 2015
    Location
    Dubai, UAE
    Posts
    89
    Yup your right....fortunately its correct on the Apex

Similar Threads

  1. Disable AWC forever until manually turned back on
    By ScooterV in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 2
    Last Post: 02-12-2017, 15:22
  2. Question: Auto setting back to auto
    By Scarface in forum Misc Apex Usage & Programming
    Replies: 2
    Last Post: 11-30-2016, 18:16
  3. Replies: 8
    Last Post: 12-03-2015, 17:15
  4. Replies: 3
    Last Post: 08-24-2013, 04:18
  5. Question: How to make float switch power off outlet until manually turned back on.
    By btaylor66 in forum Misc Apex Usage & Programming
    Replies: 2
    Last Post: 07-15-2013, 08:36

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •