    Alarm keeps going off for no reason

    I have my alarm set as the following.

    Set Off
    If SWx6_1 CLOSED Then ON

    This is my leak detector. On my dashboard it shows SWx6_1 as OPEN but my alarm keeps coming on. I also get the following text message. Any help is greatly appreciated.

    FRM:Apex Fusion
    SUBJ: Apex Fusion Alarm:
    apex
    MSGate: 2018-06-08
    19:11:55 +2000
    Status:OFF
    Statement: Set OFF

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Two things.

    1. Make sure you have these two lines in your email to filter out noise (you can adjust the time but 30 seconds is good for almost everybody)

    Defer 000:30 Then ON
    Defer 000:30 Then OFF

    2. A lot of surfaces can "confuse" the leak sensor (hardwood, concrete, linoleum) and placing a paper towel under the leak sensor can remedy that.

    Sent from my SM-G965U using Tapatalk

  3. #3
    New User
    Join Date
    Jan 2018
    Location
    Sparks NV
    Posts
    9
    I have a similar problem when ever an alarm goes off i get a ton of notifications saying it is off. Where do i add the Defer 000:30 Then ON
    Defer 000:30 Then OFF

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Nicksreef View Post
    I have a similar problem when ever an alarm goes off i get a ton of notifications saying it is off. Where do i add the Defer 000:30 Then ON
    Defer 000:30 Then OFF
    You add it to the email alarm outlet. This will only have an effect on alarms that are done through the email outlet and will not help any alarms made using the inputs tab.

    Sent from my SM-G965U using Tapatalk

  5. #5
    New User
    Join Date
    Jan 2018
    Location
    Sparks NV
    Posts
    9
    Thank you very much

Similar Threads

  1. Reason why this happens and solution COR15
    By Aquamane in forum COR-15 & COR-20 Pumps
    Replies: 0
    Last Post: 09-22-2021, 16:18
  2. Another reason the Salinity Probe malfunctions
    By Mmessing in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 0
    Last Post: 03-21-2021, 12:03
  3. Alarm with no reason???
    By jeffatpm in forum Misc Apex Usage & Programming
    Replies: 3
    Last Post: 09-18-2019, 14:01
  4. Question: New fmm created for unknown reason.
    By jonathan9573 in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 1
    Last Post: 02-18-2018, 20:25
  5. Network connection went down for no known reason!
    By woodnaquanut in forum Networking & Internet Connectivity
    Replies: 5
    Last Post: 06-18-2013, 10:22

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •