I have created a Virtual Outlet "Maintenance" so that I can do routine maintenance.
During the maintenance I want to be able to turn off my Ext_Filter without getting bombarded with email warnings because the flow has stopped, however I want to make sure that just in case something else goes wrong, i.e. I develop a leak somewhere, water level gets too low, etc that I will still get a warning for these other issues.
Is this possible?
Below is what I currently have programed for my email alarm and the ext filter.
EmailAlm_I5
Fallback OFF
Set OFF
If FLOW > 300 Then ON
If FLOW < 200 Then ON
If Output Maintenance = ON Then OFF
If pH > 8.00 Then ON
If pH < 6.90 Then ON
If Temp_1 > 80.0 Then ON
If Temp_1 < 75.9 Then ON
If Leak_L CLOSED Then ON
If Leak_R CLOSED Then ON
If H2O_Lo OPEN Then ON
Ext_Filter
Fallback ON
Set ON
If H2O_Lo CLOSED Then ON
If H2O_Lo OPEN Then OFF
If Leak_L CLOSED Then OFF
If Leak_R CLOSED Then OFF
If Output Maintenance = ON Then OFF