I am going to put a skimmate accumulation tank in service. This tank will collect excess skimmate. When somewhat full I want the sensor activate the PMUP to run approximately 0:15. Any help in programming this set up?
I am going to put a skimmate accumulation tank in service. This tank will collect excess skimmate. When somewhat full I want the sensor activate the PMUP to run approximately 0:15. Any help in programming this set up?
I wouldn't recommend using an optical sensor with skimmate. It's too likely to gunk up and misread, so a float switch is more reliable.
With that said, you want something like this
Fallback OFF
Set OFF
If Switch CLOSED Then ON
Min Time 000:15 Then ON
When On > 002:00 Then OFF
(Existing code)
If Error Outletname Then ON
This will run 15 seconds when the switch closes and if for some reason the switch is still reading closed after 2 minutes it will go to manual OFF and send you a text.
Sent from my SM-G965U using Tapatalk
thank you for that information. Which float switch would you recommend? I have the ones that would require the instalation of a breakout box and I have one that has a male plug in that is a little to large for the FMM so, I have a reducer on it and it would plug in.
What if the skimmer is going crazy? Do you want to shut it down?
Sent from my iPad using Tapatalk
That can be done with additional failsafes, but requires some initial testing first on how often "normal" is to be effective.
If for example the pump typically ran once every 3 hours then you could add a failsafe like this (assumes switch opens at high level). This would detect if the pump ran in the last 90 minutes before the switch closed again and if it did, it shuts off the skimmer for 6 hours as a precaution.
SkimTimer
Set OFF
If SkimSwitch OPEN Then ON
Defer 090:00 Then OFF
StopSkimmer
Set OFF
If SkimSwitch OPEN Then ON
If Output SkimTimer = OFF Then OFF
Defer 002:00 Then ON
Min Time 360:00 Then ON
Skimmer
(Existing code)
If Output StopSkimmer = ON Then OFF
Sent from my SM-G965U using Tapatalk