    ATK switching its self to off, also overfilling

    My ATK has been switching its self from “Auto” to “off” so that I manually have to turn it back to auto to make it fill. Then it keeps filling even after both sensors are closed (they are clean) and the only thing that kept it from overflowing was the float valve.


    Used to work fine. I am not sure what happened.
    Attached Images Attached Images

  2. #2
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    The ATK is turning itself off because the When On statement generates an error code when the water runs continuously for more than 2 minutes. You have to turn the tile back to ON briefly and then to AUTO to reset it (make sure it doesn't stay on ON, or it will keep filling.) To troubleshoot this, first, make sure that there are no mechanical problems with the pump, obstructions in the water line, or conditions predisposing to developing a siphon. Observe water flow and control by manually turning the system on and off from the tile. Also make sure that your low and high optical sensors are detecting the water level correctly. If the system is mechanically ok, it's possible that, with the coming of summer, your evaporation has increased, resulting in error generation now when the system was previously working fine. If this is the case, usual ways to solve this are to either decrease the Min Time statement to say 30 minutes to allow the ATK to pump smaller amounts more frequently, or increase the When On time to perhaps 3 minutes to let it pump for longer at each activation, and see if that fixes the situation.

Similar Threads

  1. ATK outlet on EB832 keeps switching on and off
    By Kpalas in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 1
    Last Post: 01-16-2021, 19:05
  2. Help! ATK Overfilling
    By Jay1982 in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 6
    Last Post: 11-14-2018, 20:58
  3. ATK - Overfilling ... how to uninstall ?
    By SUB-SS in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 12
    Last Post: 09-21-2018, 20:24
  4. ATK overfilling after reset
    By nullbreached in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 4
    Last Post: 04-09-2018, 08:49
  5. Atk stand alone overfilling
    By snunnelly in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 0
    Last Post: 11-05-2017, 15:29

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •