I have a VO named MAN_WC that among other things, turns off EmailAlarms so that when the probes are out of the water in the display tank I don't get alarm notices for pH, Temp, Salinity. When MAN_WC is OFF the display equipment comes on with the return pump first, followed by the skimmer after a delay then the Jebao power heads after another delay period. I'd like to add a defer statement to the Alarms output but don't know if I should say Defer 010:00 Then ON or do I say Defer 010:00 Then OFF? If I say ON will it put the output to ON and send out an email and text alert or will it continue down the program list and when it comes to Set OFF turn off? My programming of this Output is as follows.
Set OFF
If skmFul OPEN Then ON
If Smp_Lo CLOSED Then ON
If SmpHI OPEN Then ON
If T_TEMP > 81.0 Then ON
If T_TEMP < 74.0 Then ON
If T_Salt < 32.5 Then ON
If Ret_HI CLOSED Then ON
If VSVFil CLOSED Then ON
If T_NSW > 80.0 Then ON
If Error Ret_High_VO Then ON
If Error ATO_4_4 Then ON
If Output MAN_WC = ON Then OFF
If Error AWC_LO_VO Then ON
Let me know what you think. Thanks.