    Reservoir Programming help

    Hello I have a 160 gal reservoir that I'm installing a FMM and a apex solenoid switch connected to my RODI and I need some programming help. The program that I tried from other users on the forum isn't working.


    Fallback OFF
    If Swx6_1 OPEN Then ON (swx6_1 = Low optical switch)
    If Swx6_2 CLOSED Then OFF (swx6_2 = Hi optical switch)
    Defer 000:05 Then ON

    I need a Program that says when the water goes below the low switch the solenoid turns on and ONLY turns off when both the HI and Low switch is covered by water. At the moment the FMM is turning off when either of the optical switches are under water.

    And before someone says it yes I would like to change the names of the optical switches but I don't know how to do it in apexfusion.

    Any help with this would be appreciated.
    Thanks jtspeedy

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Sounds from your description like you added a set OFF by mistake that you forgot to post. If so remove that. If that is not the case, make sure your cables are pushed in all the way as this can cause similar behavior if they are a tiny bit loose.

    To change the name, click the icon that looks like a thermometer then select the switch in that inputs page and you can rename there.



    Sent from my SM-G965U using Tapatalk

  3. #3
    New User
    Join Date
    Jun 2018
    Location
    US, Eastern Time
    Posts
    9
    I posed exactly what I have for programming and it not working.

    Sent from my SAMSUNG-SM-G935A using Tapatalk

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    If that is the code that is uploaded, the code itself is fine. The problem is somewhere in the setup. Double check that the low is plugged into 1 and the high in 2. Reseat and make sure they click when you insert them and that their states show correctly in fusion (covered = closed).

    Sent from my SM-G965U using Tapatalk

  5. #5
    New User
    Join Date
    Jun 2018
    Location
    US, Eastern Time
    Posts
    9
    I reset the fmm and now it is working as I need it to.

    I'm not finding the thermometer icon in apex fusion, this is the apex classic I have does it make a difference weather is the classic or new version?

    Sent from my SAMSUNG-SM-G935A using Tapatalk

  6. #6
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Your profile said 2016, so those instructions were for that. For the apex classic, you need to go to the classic dashboard and then navigate to the probe setup page.

    Sent from my SM-G965U using Tapatalk

Similar Threads

  1. solenoid and ato reservoir programming
    By ask499 in forum Misc Apex Usage & Programming
    Replies: 4
    Last Post: 04-30-2022, 10:02
  2. RO Reservoir Programming Help!
    By SteveHJ in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 6
    Last Post: 05-06-2021, 03:50
  3. RO/DI Reservoir Programming Review
    By capitalaquariums in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 3
    Last Post: 07-15-2020, 13:34
  4. Help! Ro reservoir programming
    By Jbaker2290 in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 6
    Last Post: 06-30-2016, 06:12
  5. ATO Reservoir Programming
    By mund in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 1
    Last Post: 02-06-2014, 14:18

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •