Hello all!
Will you please let me know if this is good to go:
Tunze- Outlet 1
Fallback ON
Set ON
If FeedA 015 Then OFF
If FeedB 015 Then OFF
This is a powerhead. I want it on 24/7, unless either feed modes are engaged. I want the pump to shut of in those cases for 20 minutes, and then turn back on.
Koralia-Outlet 2
Same as above.
Return Pump- Outlet 3
Fallback ON
Set ON
If FeedA 015 Then OFF
If FeedB 015 Then OFF
This is my sump return pump. I want it on 24/7, unless either feed modes are engaged. I want the pump to shut off in those cases for 20 minutes, and then turn back on.
Heater- Outlet 4
Fallback OFF
If Tmp < 77.1 Then ON
If Tmp > 77.9 Then OFF
If Tmp < 75.0 Then OFF
I want it to be off if the head unit isn't connected to the energy bar, to turn on at 77, off at 78. The last line is my failsafe, should the probe stop working, I want the temp off.
Skimmer- Outlet 5
Fallback ON
Set ON
If FeedB 015 Then OFF
I want it on 24/7, unless feed mode b is engaged. Then I want it to turn back on 20 minutes later.
Refuge Light-Outlet 7
Fallback OFF
Set OFF
If Time 21:00 to 08:00 Then ON
If Tmp > 80.0 Then OFF
I want the light to be off if the head unit is disconnected, and to only come on between 9pm and 8am. If the temp gets above 80, I want it to turn off, and then back on if it goes below 80.
Fan- Outlet 8
Fallback OFF
If Tmp > 80.0 Then ON
If Tmp < 79.0 Then OFF
I want the fan to be off if the head unit is disconnected, and I want the fan to turn on in the sump if temp gets to 80, and off at 79.
Really hoping I got this right!
Bill